Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82258members
349811posts

PID function block for SP 474

Remote Operations Forum

Collaborate and share knowledge on the extensive range of remote systems and devices, including SCADA radios and RTUs, on the Schneider Electric Exchange Remote Operations (formerly SCADA & Telemetry) forum. From commissioning SCADA integration devices and software, to enhancing existing installations or troubleshooting, connect with a global community of experts and users. Subscribe today.

Solved
mike723
Crewman
Crewman
0 Likes
2
266

PID function block for SP 474

What would be the equivalent PID function block in RemoteConnect to a PIDA function block in Telepace Studio?

 


Accepted Solutions
MartinChartrand
Captain Captain
Captain

Re: PID function block for SP 474

Hello,

In RemoteConnect's SCADAPack x70 Documentation Set > Porting Guide for Telepace to SCADAPack RemoteConnect > Appendix > Telepace Elements Compatibility Chart

 

You'll find PIDA in Telepace is equivalent to PI_B and PIDFF in RemoteConnect.

 

Thank you.

Martin

 

 

 

See Answer In Context

2 Replies 2
MartinChartrand
Captain Captain
Captain

Re: PID function block for SP 474

Hello,

In RemoteConnect's SCADAPack x70 Documentation Set > Porting Guide for Telepace to SCADAPack RemoteConnect > Appendix > Telepace Elements Compatibility Chart

 

You'll find PIDA in Telepace is equivalent to PI_B and PIDFF in RemoteConnect.

 

Thank you.

Martin

 

 

 

mike723
Crewman
Crewman
0 Likes
0
257

Re: PID function block for SP 474

Thanks Martin,