[Imported] How do you make the totalized value retained after a power cycle.
Remote Operations Forum
Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-10-2503:47 PM
[Imported] How do you make the totalized value retained after a power cycle.
>>Message imported from previous forum - Category:SCADAPack RTU<< User: mchartrand, originally posted: 2018-10-25 14:20:22 Id:211 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.
_______
**_instr: I am using a Scadapack350 to totalize condensate flow to a boiler. This totalized value is reset to zero everytime a power cycle happens in the plant. Is there a function block i can use that will retain the value._**
______________
bevanweiss: Do you have the variable set to RETAIN'd? (and within the range of addresses that will be retained)