ISAGRAF APPLICATION ERROR
Hi everyone,
- Isagraf shows me an application error, not sure what causes the error, I've tried changing the .dll file ,but still no luck. Response from you guys will be really helpful.(Attached the image of the error)
- We use isagraf for our schneider scadapack 357& 32 , but schneider says that they don't provide technical support for isagraf, so what is schneider's software like isagraf(to communicate with the plc)?
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-24 12:08 PM
You'll need to provide more information.
What virtualisation platform are you currently using? (WindowsXP Mode, or VMWare, or HyperV, or other)
What Host OS are you using?
What Guest OS are you using?
What have you tried so far?
I assume you googled, and tried all of the suggestions from here:
Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-22 07:58 AM . Last Modified: 2021-10-22 08:17 AM
Hello Tharun,
We've looked into this situation and there's really not a lot to be done. The very old (and no longer supported) 16-bit ISaGRAF software is running on a 64-bit computer, perhaps in a 32-bit VM, and there's just no way to ensure it continues to operate reliably.
The best solution is to upgrade to Workbench. If you need assistance finding a sales representative in your region, let us know. You can download the software from our Exchange Shop, but a license must be purchased. Here's how to get the software:
- Open the website exchange.se.com
- Click the Register button and complete the very easy registration
- Perform a search for SCADAPack Workbench
- Select either SCADAPack Workbench or SCADAPack E Workbench, depending on the type of RTU's you have
- Download the software after reading the entire page. Note this comment part-way down the page:
Important: The software installation package is available here as a free download. However a license (to be purchased separately) is required for full operation. Please select the “Contact Us” button or contact your local Schneider Electric sales partner directly for further details.
Remote Operations Specialist
Schneider Electric
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-24 12:08 PM
You'll need to provide more information.
What virtualisation platform are you currently using? (WindowsXP Mode, or VMWare, or HyperV, or other)
What Host OS are you using?
What Guest OS are you using?
What have you tried so far?
I assume you googled, and tried all of the suggestions from here:
Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..