Posted: 2019-12-19 05:21 AM
The device status of Accutechs can be added together. You are getting a 1 + 2048. If memory serves correctly, 2048 is a code indicating that the configuration of the device was changed through the buttons on the unit. It's not a bad thing, just informational. More details can be found in the free Accutech Manager software's help files.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-19 05:21 AM
The device status of Accutechs can be added together. You are getting a 1 + 2048. If memory serves correctly, 2048 is a code indicating that the configuration of the device was changed through the buttons on the unit. It's not a bad thing, just informational. More details can be found in the free Accutech Manager software's help files.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-19 05:32 AM . Last Modified: 2019-12-19 05:33 AM
But in my E configurator, it shows Engineering unit exceeded when reading the DNP3 point, do i adjust the engineering unit to accomodate this value or is there a way that i can split this to get my 1 seperate from the 2048?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-19 06:22 AM
Yes. You will have to lookup what the maximum range of the value could be from the Accutech Manager software help file which I can't seem to find using google right now.