Digital inputs scan faster on the SCADAPack 575 I/O board than on the Controller?
Remote Operations Forum
  • Remote Operations
  • Remote Operations Forum
  • Digital inputs scan faster on the SCADAPack 575 I/O board than on the Controller?
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
Jimi
Commander Jimi Commander
Commander
Posted: ‎2019-11-21 07:03 AM
2607
Customer support question:
I found this in the SCADAPack 5xx manual:
Controller board => Timestamping => 10ms Sequence of Event (SOE)
I/O board => 1ms Sequence of Event (SOE)
Why is this? It seems like a mistake in the manual? Is it correct that the SOE on the IO board is faster than on the CPU? Seems illogical.
  • DNP3
  • Logic
  • RTU
  • SCADA
  • Telemetry
Jimi
Commander
The manual is correct since the IO board is dedicated to handle timestamping at 1ms resolution.
The 575 controller board is operating on 1 core only which requires all executing tasks to be shared.
BevanWeiss
Spock BevanWeiss
Spock
Posted: ‎2019-11-27 01:03 AM
As @Jimi said, the IO on the 'CPU' board is not really targeted for use beyond as auxiliary IO.  These two inputs (and one output) are available on both the 570 and the 575.  If you require high speed detection then the dedicated IO boards (575 base IO, or 6601 IO) would be the recommended way forward.
Jimi
Commander
BevanWeiss
Spock BevanWeiss
Spock