Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Wireless Communication Options: Part 5

Remote Operations Blog

Read announcements related to Remote Operations (formerly SCADA & Telemetry). New products, new versions, case studies, videos and other relevant news will be posted in this blog. Keep up-to-date with the challenges that remote sites present and how to ensure reliable communications, monitoring & management to enhance productivity and profitability.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Blog
  • Wireless Communication Options: Part 5
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • SCADA 114
  • Telemetry 113
  • RTU 60
  • IoT 42
  • Logic 32
  • DNP3 28
  • Drivers 16
  • Radio 16
  • Scripting 9
  • ViewX 9
  • Virtual ViewX 8
  • Mimics 7
  • Trends 5
  • WebX 5
  • WITS 5
  • Redundancy 3
  • Previous
  • 1 of 2
  • Next
Latest Blog Posts
  • Geo SCADA 2025 is now available
  • EcoStruxure Control Expert 16.0 (Logic Editor)
  • Updates to Geo SCADA Mobile are coming - warning of action needed
  • Release Announcement: EcoStruxure RTU Operations Expert (EROE)
  • Release Announcement: RemoteConnect 3.3.3
Related Products
product field
Schneider Electric
Trio Licensed Radios
product field
Schneider Electric
SCADAPack 57x
product field
Schneider Electric
SCADAPack 47x

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Joel_Weder
Captain Joel_Weder Captain
Captain
‎2022-04-29 11:45 AM
1 Like
1
1584
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-29 11:45 AM

Wireless Communication Options: Part 5

Originally published on Remote Operations Blog by Joel_Weder | April 29, 2022 08:45 PM

Cybersecurity Features

It must be understood by those implementing a modern IP-based wireless system that it will be part of a network, and network security is of vital importance to end users. Before any system is purchased, the security requirements must be understood and included in the project. This is one reason that IT professionals are today more commonly involved in the design, installation and operation of any wireless system.

 

Cyber-crime is one of the fastest-growing and lucrative illegal activities. Both private individuals and foreign government agencies are involved in attacks. Many of the projects in which industrial wireless offers are incorporated include monitoring and control of critical infrastructure. It is vital that communication media employed on such projects provide a high degree of protection from cyber-attacks.

 

As the sophistication and frequency of attacks increase, so also must the investment in wireless cybersecurity tools. Some inherent security capability exists with wireless devices, as hackers may not initially know the operating frequency or configuration details. However, clever hackers may be able to use a spectrum analyzer to determine frequency, may steal a configured radio, or access a network drive containing the system configuration files.

 

The better data radios today include many features for cybersecurity purposes, including multi-user authentication and access logs, AES-GCM encryption, Radio Access Control, sophisticated filtering firewalls, the ability to disable unused ports, HTTP Secure access and more. The threat must however be monitored constantly, and new features added as necessary, to ensure each system remains well able to defend against attacks. Additional tools must be considered as the threat level increases. For example secure configuration files, firmware tamper protection, two-factor Radius Authentication and more.

 

Older wireless devices, whether new or already installed, may have fewer tools for cybersecurity - a single login password perhaps, AES128 or 256 encryption, not much more. It may be argued that frequency hopping is a security feature, but if a radio or its configuration file is acquired by a bad actor this is of no assistance. These older systems need to be evaluated for potential threat level, and to see if any interim mitigation strategies can be implemented to extend their lifespan.

 

When designing any project which includes IP-based connectivity, wireless or not, the other devices in the system must also include features to protect against cyber attacks. RTU's, PLC's and other field devices must be secured against intrusion and protected against exploits such as Denial of Service (DoS) attacks. Connected computers (e.g. SCADA Hosts) must be well protected with tools such as firewalls and anti-virus software, and must be isolated from the Internet. And perhaps most importantly, all staff must be well educated to understand the threat environment.

 

 

Value-Added Features

Industrial wireless vendors are increasingly offering optional capabilities. There is strong competition from devices such as cellular, satellite and high-data-rate solutions, which may be less expensive to purchase, or may offer higher data rates. It must be noted that the lower-frequency narrow-band licensed radios and license-free devices do provide some inherent benefits, such as better ability to handle complex terrain, but often this is not the deciding factor.

 

One feature being offered by some vendors is to include two or more different wireless modules within a single housing.  Modules offered might be VHF or UHF licensed, 900 MHz or 2.4 GHz license-free, industrial WiFi or cellular. This concept may assist in projects where installation space in equipment enclosures is very limited. However, it can be more difficult than with separate devices to change one to a different technology. Also, if one module fails the entire unit may need to be replaced.

 

Several manufacturers are now offering radios with a small amount of on-board I/O for monitoring or control. There may just be a couple of digital I/O points, or there may be a larger mix of digital and analog points. Certain manufacturers include expansion I/O modules which can be easily attached to the radio, to grow the I/O as system requirements change at different sites or over time. Depending on the vendor, the I/O may be accessed through a standard protocol such as Modbus, or it may require a proprietary interface.

 

And in a related development, some models may be purchased with an operating system (separate from the radio's functionality) which allows for 3rd party Linux-based applications to be run. It seems clear that there is a trend towards merging the capabilities of the RTU and radio. An offsetting factor, however, is that many customer applications demand low power consumption. Processors must be powerful and yet operate on a tiny power budget.

 

Manufacturers are moving to highly flexible hardware and device operating systems, capable of a very wide range of data rate depending on link demands and challenges. (e.g. 56 kbps to 4 Mbps in a single model) Also some include the capability to switch between license-free and licensed within a single module, though using only one at a time. This can be done more easily with new models due to the increasing use of SDR (software-defined radio) technology.

 

Earlier wireless systems were designed, installed and maintained by highly skilled and experienced experts. As those workers retire, however, there is a growing gap in the workforce’s ability to specify, design, install and maintain complex wireless systems. Younger workers interested in high-tech are tending to choose careers in other fields. As a result, there is a strong push towards new devices which are simple to configure, and easy to maintain. Some vendors offer configuration "Wizard" modes which anticipate typical configuration scenarios, and Youtube videos have become quite popular for basic instruction. 

 

 

Summary

With the increasing complexity of wireless devices, combined with the demand to reduce cost, some manufacturers have left the remote SCADA and Telemetry market as they are not able to compete. Despite this, others are rising to fill the gap, often offering products with “outside the box” thinking, as discussed above. And multiple new LEO satellite providers have appeared within just a few years. Clearly there is still room for growth.

 

The wireless industry is in flux due to rapidly increasing demands, as well as dramatic changes in available technologies. While the wireless “world of tomorrow” will retain many of the aspects we understand today, there will be new requirements and more tools to meet those requirements. It is vital to begin to at least consider these demands now, to avoid being overwhelmed by the complex array of options.

 

One thing is clear – wireless is not going away. In fact the industry is growing. The landscape is changing, faster than ever, but there are many areas for improvement in reliability, data rates, cybersecurity and innovative features to help wireless system operators.

 

Labels:
  • Radio

  • RTU

  • SCADA

  • Telemetry

Author

Biography

Joel_Weder

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
1 Comment

Would you like to add a comment?

All registered members have full access to the Community and can post comments and start topics.

  • Sign in / Register
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore