Hi all,
I’m running an PowerLogic T500 (HU280 + DI180 + DO180) with Easergy Builder v1.7.49 as an IEC-104 slave (ASDU addr = 1, port 2404).
What works
Telemetry is fine: analogs and double-point DIs come through over 104.
From the web UI, Force DO works — relays click, so hardware is OK.
The issue
From an IEC-104 tester, sending TI=46 (C_DC_NA_1 / Double Command) does not operate the DOs.
In the trace I see COT=6 (activation) followed by “7: negative activation confirmation” (no termination). The relay doesn’t move.
What I’ve tried
104 Enable = ON.
CMD use act term = ON, CSE use act term = ON.
In Control Points, C_DC is enabled; tried both Direct Execute and Select→Execute (SBO).
In coreDB → Command, IOAs 160–167: CDC are mapped to DO180 channels (Latch = N, ExeTim = 500 ms).
Question
Is there any T500-specific setting or trick required to make TI=46 Double Command drive the DOs?
If the T500 expects particular QOC/QU/Select bit combinations, could you share a working example frame?
Also, is there a global Secure / Block controls option that might be rejecting C_DC commands?
Thanks a lot! 🙏
Link copied. Please paste this link to share this article on your social media post.
Hi all,
Just a quick update to close the thread — I’ve finally identified the cause and the issue is now resolved.
The problem was related to the Select Before Operate (SBO) mode. The IEC-60870-5-104 tester I was using had “SBO mode” enabled, and at the same time, the “Select before operate” checkbox in Easergy Builder (under output configuration) was also checked.
At first, I thought that checkbox only affected specific 104 output modes, but when I hovered over it, the tooltip clearly described it as the Select Before Operate feature. Once I disabled this option, the DOs successfully operated when commanded from the 104 tester. With the option enabled, the relays didn’t respond.
Later, I tried a different 104 tester and found that it worked even in SBO mode — so the behavior actually depends on the tester implementation.
Thanks everyone for your input and comments. Hopefully this helps others who encounter the same situation.
Link copied. Please paste this link to share this article on your social media post.
Hi @JuanRayo , could you please help @OdysseiaTiTi with these questions about T500?, thx.
Link copied. Please paste this link to share this article on your social media post.
Hello @OdysseiaTiTi .
There is no trick at all.
Please share with us your Easergy Builder configuration and some wireshark traces captured when the command failed.
BR
Link copied. Please paste this link to share this article on your social media post.
Sorry for the delay , I do not know why this topic did not reach our inbox sooner.
Link copied. Please paste this link to share this article on your social media post.
Hi all,
Just a quick update to close the thread — I’ve finally identified the cause and the issue is now resolved.
The problem was related to the Select Before Operate (SBO) mode. The IEC-60870-5-104 tester I was using had “SBO mode” enabled, and at the same time, the “Select before operate” checkbox in Easergy Builder (under output configuration) was also checked.
At first, I thought that checkbox only affected specific 104 output modes, but when I hovered over it, the tooltip clearly described it as the Select Before Operate feature. Once I disabled this option, the DOs successfully operated when commanded from the 104 tester. With the option enabled, the relays didn’t respond.
Later, I tried a different 104 tester and found that it worked even in SBO mode — so the behavior actually depends on the tester implementation.
Thanks everyone for your input and comments. Hopefully this helps others who encounter the same situation.
Link copied. Please paste this link to share this article on your social media post.
Thanks for your feedback on behalf of the community..
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.