PowerLogic T500 - Mapping multi Status points to one holding register in Modbus Slave

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T500 - Mapping multi Status points to one holding register in Modbus Slave
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
MinQV
Crewman MinQV
Crewman

Posted: ‎2025-08-18 03:09 AM . Last Modified: ‎2025-08-25 05:49 AM

0 Likes
3
517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-18 03:09 AM

PowerLogic T500 - Mapping multi Status points to one holding register in Modbus Slave

Dear Experts,

 

I'm using the T500 module to collect data from DI/DO/DO modules. Now I want to create a Modbus Slave for others to read values. With "Status" points, do we have any way for mapping multiple points to one holding register?

 

Labels
  • Labels:
  • PowerLogic T500
Tags (4)
  • Tags:
  • english
  • modbus
  • PowerLogic T500
  • slave Modbus device
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JuanRayo
Lt. Commander JuanRayo Lt. Commander
Lt. Commander

Posted: ‎2025-08-25 02:16 AM

0 Likes
1
490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-25 02:16 AM

Hello MinQV.

 

Yes you can .

 

using Formulas you will be able to gather different booleans in just one package to be sent upstream as a holding register .

I am attaching an example where some booleans (from IEC61850) are multiplied by a factor (1*, 2*, 4*, 10*,....) which determine the position in the holding register to be transferred. Hope this suits your needs.

 

JuanRayo_0-1756113177736.png

 

See Answer In Context

Reply
Replies 3
JuanRayo
Lt. Commander JuanRayo Lt. Commander
Lt. Commander

Posted: ‎2025-08-25 02:16 AM

0 Likes
1
491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-25 02:16 AM

Hello MinQV.

 

Yes you can .

 

using Formulas you will be able to gather different booleans in just one package to be sent upstream as a holding register .

I am attaching an example where some booleans (from IEC61850) are multiplied by a factor (1*, 2*, 4*, 10*,....) which determine the position in the holding register to be transferred. Hope this suits your needs.

 

JuanRayo_0-1756113177736.png

 

Reply
MinQV
Crewman MinQV
Crewman

Posted: ‎2025-08-25 08:20 PM

0 Likes
0
479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-25 08:20 PM

Hello JuanRayo,

Thank you for your advice. Regarding the factors, I saw that you use 10, 20, and 40. Where can I find this value for the formula?

Reply
JuanRayo
Lt. Commander JuanRayo Lt. Commander
Lt. Commander

Posted: ‎2025-08-26 12:06 AM

0 Likes
0
472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-26 12:06 AM

Hello MinQV.

 

Basically the multiplier factor is in Hexadecimal if you convert it into binary you´ll see the bit/position in the word where the boolean signal will be located.

 

JuanRayo_0-1756191849553.png

 

Here you are the factors.....you can check then out with a calculator: 1,2,4,8,10,20,40,80,100,200,400,800,....

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore