Dear Experts,
I'm using the T500 module to collect data from DI/DO/DO modules. Now I want to create a Modbus Slave for others to read values. With "Status" points, do we have any way for mapping multiple points to one holding register?
Link copied. Please paste this link to share this article on your social media post.
Hello MinQV.
Yes you can .
using Formulas you will be able to gather different booleans in just one package to be sent upstream as a holding register .
I am attaching an example where some booleans (from IEC61850) are multiplied by a factor (1*, 2*, 4*, 10*,....) which determine the position in the holding register to be transferred. Hope this suits your needs.
Link copied. Please paste this link to share this article on your social media post.
Hello MinQV.
Yes you can .
using Formulas you will be able to gather different booleans in just one package to be sent upstream as a holding register .
I am attaching an example where some booleans (from IEC61850) are multiplied by a factor (1*, 2*, 4*, 10*,....) which determine the position in the holding register to be transferred. Hope this suits your needs.
Link copied. Please paste this link to share this article on your social media post.
Hello JuanRayo,
Thank you for your advice. Regarding the factors, I saw that you use 10, 20, and 40. Where can I find this value for the formula?
Link copied. Please paste this link to share this article on your social media post.
Hello MinQV.
Basically the multiplier factor is in Hexadecimal if you convert it into binary you´ll see the bit/position in the word where the boolean signal will be located.
Here you are the factors.....you can check then out with a calculator: 1,2,4,8,10,20,40,80,100,200,400,800,....