New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Saitel DP - Power supply redundancy?
Protection & Control
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2025-07-3003:43 AM
Saitel DP - Power supply redundancy?
Hi,
Currently i am working on a project, I've two Power supplies of type SM_PS40/A5 connected to a backplane of type SM_BPX/9. when powering up the RTU, Only Power supply providing the power to RTU, if its disconnected then the RTU gets off. how to make the Power supplies to be redundant?.
Link copied. Please paste this link to share this article on your social media post.
2025-08-2503:05 AM
Hello Mohamed.
In a redundant configuration, the first Power Supply is connected to the slot 1 in the backplane and the second PS module to the slot 2. So first of all check out that both PS are working fine individually and then insert them like in the picture below.
No further configuration would be needed. I hope this helps you.
Link copied. Please paste this link to share this article on your social media post.
2025-08-2503:05 AM
Hello Mohamed.
In a redundant configuration, the first Power Supply is connected to the slot 1 in the backplane and the second PS module to the slot 2. So first of all check out that both PS are working fine individually and then insert them like in the picture below.