Dears.
T300 catalogue proposes 24Ah and 38Ah batteries, going with PS50 secure power supply.
Some customers have extra requirements (e.g. high consuming routers) or asking for very large batteries by habit. Is it possible with PS50 to manage batteries of higher capacity and how?
Distribution Automation Senior Application Engineer
- Labels:
-
PowerLogic T300
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello,
PowerLogic T300 with powersupply PS50 can be used with other batteries than the references proposed in the T300 catalog.
Here are some notes on how to adapt the settings to a different capacity and optimize the management of the battery.
Mathieu Lansoy.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello,
PowerLogic T300 with powersupply PS50 can be used with other batteries than the references proposed in the T300 catalog.
Here are some notes on how to adapt the settings to a different capacity and optimize the management of the battery.
Mathieu Lansoy.