Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Micom P139 No Disturbance record detected

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Micom P139 No Disturbance record detected
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
60
Arun-kumar_PS
Arun-kumar_PS Mentor
26
JuanRayo
JuanRayo Mentor
24
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Muhammad_Hassan
Muhammad_Hassan
Explorer

Posted: ‎2023-12-19 10:18 PM

0 Likes
3
2491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-19 10:18 PM

Micom P139 No Disturbance record detected

The relay does not show any disturbance record when connected through Serial Communication.
The relay performed the tripping action due to an actual fault, but still no disturbance record detected.

Moreover, the relay does not record the value of IN> on primary and secondary in FT_RC.

The relay also does not show any GF_RC on actuation of IN>.

Labels
  • Labels:
  • MiCOM range
Tags (1)
  • Tags:
  • Micom P139
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Rudolf_Simon
Rudolf_Simon Leader
Leader

Posted: ‎2024-01-29 11:18 PM

0 Likes
0
2315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-29 11:18 PM

Hello Hassan,

I assume the fault duration was too short to allow fault locator operation.

If possible, you may share the recording and setting files with L3 (Boguslaw.Wilczynski@se.com) or myself (Rudolf.Simon@se.com) for more detailed review.

Best regards

Rudolf

See Answer In Context

Reply
Replies 3
Rudolf_Simon
Rudolf_Simon Leader
Leader

Posted: ‎2024-01-02 10:59 AM

0 Likes
2
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-02 10:59 AM

Hello Muhammad,

 

Disturbance recording trigger conditions have to be set at “FT_RC: Fct. Assig. trigger” [MPA 060 000] in menu “Parameters/ Function parameters/ Global/ FT_RC”. By default, no trigger is assigned.

 

Your 2nd question is not clear to me: “the relay does not record the value of IN> on primary and secondary in FT_RC.”

IN> is a threshold setting in neutral OC protection element(s); and settings are not recorded along a disturbance.

Measured values from last fault are available in menu “Events/ Measured fault data/ FT_DA”. There are measured and calculated neutral current values in per unit and primary Ampere [MPAs 004.049, 024.217, 010.216, 024.218].

Note, that these values are only evaluated, if a phase-ground loop is selected, hence for A-G or B-G or C-G faults. For phase-phase or 3-phase faults, no neutral current is evaluated.

 

GF_RC is a specific solution to log just events from GFDSS and TGFD in a file. These at are dedicated functions to detect ground faults in systems with isolated or compensated starpoint; usually for direction indication only, not for tripping (a ground fault in such systems is no short-circuit, just a displacement of neutral point).

GF_RC is independent from FT_RC, and contains no recording of sampled signals.

In case of neutral OC IN> operation, the disturbance recording (FT_RC) and fault data acquisition (FT_DA) should be used.

 

Best regards

Rudolf

Reply
Muhammad_Hassan
Muhammad_Hassan
Explorer

Posted: ‎2024-01-28 09:09 PM

0 Likes
1
2321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-28 09:09 PM

In the last fault data in menu “Events/ Measured fault data/ FT_DA", the neutral current shows "Not Measured" in per unit as well as primary.

Although the relay performed tripping action due to an earth fault.

Reply
Rudolf_Simon
Rudolf_Simon Leader
Leader

Posted: ‎2024-01-29 11:18 PM

0 Likes
0
2316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-29 11:18 PM

Hello Hassan,

I assume the fault duration was too short to allow fault locator operation.

If possible, you may share the recording and setting files with L3 (Boguslaw.Wilczynski@se.com) or myself (Rudolf.Simon@se.com) for more detailed review.

Best regards

Rudolf

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore