Dears.
PowerLogic T300 catalog gives the choice to use either a 12 V/ 24 Ah battery or a 12 V/ 38 Ah with Easergy PS50 Secure Power Supply.
However, some customers may have either extra requirements (e.g., high-consuming 4G routers), or are just used to have very large battery capacity.
Is it possible for PS50 to manage batteries of higher capacity and if yes, how?
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes, Easergy PS50 can use a 12 V battery with a capacity higher than the standard 38 Ah (which is the highest value proposed in PowerLogic T300 catalog).
Here are some notes to describe how to adapt the settings to a different capacity and optimize the management of the battery.
Mathieu Lansoy.
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes, Easergy PS50 can use a 12 V battery with a capacity higher than the standard 38 Ah (which is the highest value proposed in PowerLogic T300 catalog).
Here are some notes to describe how to adapt the settings to a different capacity and optimize the management of the battery.
Mathieu Lansoy.