PowerLogic T300 - Issue when reading analog data from PowerLogic P3

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - Issue when reading analog data from PowerLogic P3
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All
Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
John_Archer1
Ensign John_Archer1
Ensign

Posted: ‎2024-11-22 01:11 AM . Last Modified: ‎2025-01-24 12:14 AM

0 Likes
5
791
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-22 01:11 AM

PowerLogic T300 - Issue when reading analog data from PowerLogic P3

The analog value I am reading has a minus sign (-) and an incomplete value. What settings am I making a mistake in? Has anyone had this problem? I am 

 

Read setting t300Read setting t300IEC101 settingIEC101 settingP3 Line voltage Measured valueP3 Line voltage Measured valueP3 scale settingP3 scale settingT300 Reading voltage view webserverT300 Reading voltage view webserver

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • IEC61850
  • PowerLogic P3
  • PowerLogic T300
  • Training
Tags (2)
  • Tags:
  • english
  • PowerLogic T300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mathieu_Lansoy
Lt. Commander Mathieu_Lansoy Lt. Commander
Lt. Commander

Posted: ‎2024-12-12 06:00 AM . Last Modified: ‎2025-01-24 12:25 AM

0 Likes
0
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-12 06:00 AM

Hello,

In standard, MMEB format should transmit signed 16-bit values (so from -32768 to + 32767).

These measurements will be managed in this format by PowerLogic T300 if they have been declared as MMEB.

Apparently, the P3 uses unsigned 16-bit values (from 0 to 65536) and does not scale down the values.

1. If the value is less than 32767, no issue.

2. If the value is higher than 32767, the most significant bit of the 16-bit format will be set and treated as a negative sign by T300. This explains the values shown on T300 WebApp (see example below).

Ex:  33933 V -> 0x848D -> -31603 (signed 16-bit value).

 

 

If no scaling system can be found on the P3, we can use PowerLogic T300 logic formulas to correct the value, by adding 65535 to the negative values (see below):

Mathieu_Lansoy_0-1734011096610.png

 

Another idea: use the "normalized" (MMEA) format proposed by P3 (but I don't know how the conversion can be done in this case - maybe using the corresponding "Max" setting that can be seen on the "IEC 60870-5-101: AI" page.

Mathieu_Lansoy_1-1734011669817.png

 

regards,

 

Mathieu.

See Answer In Context

Reply
Replies 5
sathishkumar_ramakrishnan
Ensign sathishkumar_ramakrishnan Ensign
Ensign

Posted: ‎2024-12-02 11:04 PM

1 Like
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-02 11:04 PM

Hello John Archer,

In MMEB the value stored in coreDb is converted in a 16-bit entire signed value. So once it exceeds the 16 bit range,it throws the negative value. Hence you need to change the phase voltage AB, BC and CA data type as MMEC which is 32 bit floating value has wide range.

If you want to use the data type as MMEB only, then you need to scale down the value to 16 bit range.

Regards,

Sathish

 

Reply
John_Archer1
Ensign John_Archer1
Ensign

Posted: ‎2024-12-04 06:25 AM . Last Modified: ‎2025-01-24 12:16 AM

0 Likes
1
703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-04 06:25 AM

@sathishkumar_ramakrishnan Thanks for the reply. The Easergy Relay I am using only reads MMEB values. How do I change from 32-bit to 16-bit value? Also, the measurement format is not normalized and does not transmit analog information at all.

Reply
sathishkumar_ramakrishnan
Ensign sathishkumar_ramakrishnan Ensign
Ensign

Posted: ‎2024-12-11 03:18 AM . Last Modified: ‎2025-01-24 12:20 AM

0 Likes
0
682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-11 03:18 AM

Hello John,

I have tested this MMEB values of the PowerLogic P3 relay with the TMW 101master [ Simulator tool], thus taking PowerLogic T300 out of the equation: the phase voltage values are displayed negatively (see attached screen shot of the same).

The Easergy Pro software will show the correct value, since it is not the standard protocol implementation tool. As I mentioned earlier MMEB datatype is a 16-bit value only: hence its showing negative values once it crosses the range.

From P3 relay, using a scaling factor is needed to provide the 16-bit data to T300 or to any IEC101 master device integration for correct data representation. However, I have not been able to find information regarding the scaling factor for P3 relay.

Regards,

Sathish

Attachments
Reply
Mathieu_Lansoy
Lt. Commander Mathieu_Lansoy Lt. Commander
Lt. Commander

Posted: ‎2024-12-12 06:00 AM . Last Modified: ‎2025-01-24 12:25 AM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-12 06:00 AM

Hello,

In standard, MMEB format should transmit signed 16-bit values (so from -32768 to + 32767).

These measurements will be managed in this format by PowerLogic T300 if they have been declared as MMEB.

Apparently, the P3 uses unsigned 16-bit values (from 0 to 65536) and does not scale down the values.

1. If the value is less than 32767, no issue.

2. If the value is higher than 32767, the most significant bit of the 16-bit format will be set and treated as a negative sign by T300. This explains the values shown on T300 WebApp (see example below).

Ex:  33933 V -> 0x848D -> -31603 (signed 16-bit value).

 

 

If no scaling system can be found on the P3, we can use PowerLogic T300 logic formulas to correct the value, by adding 65535 to the negative values (see below):

Mathieu_Lansoy_0-1734011096610.png

 

Another idea: use the "normalized" (MMEA) format proposed by P3 (but I don't know how the conversion can be done in this case - maybe using the corresponding "Max" setting that can be seen on the "IEC 60870-5-101: AI" page.

Mathieu_Lansoy_1-1734011669817.png

 

regards,

 

Mathieu.

Reply
John_Archer1
Ensign John_Archer1
Ensign

Posted: ‎2024-12-14 12:06 AM

1 Like
0
616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-14 12:06 AM

thank you guys @Mathieu_Lansoy @sathishkumar_ramakrishnan 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of