Hello
After upgrading a T300 from version 2.7 to 2.9 which had a security configuration loaded through Cybersecurity Administration Expert, it seems not so direct to connect again with CAE
How to proceed?
Link copied. Please paste this link to share this article on your social media post.
Difficulty is linked to more security added between CAE and T300, with an additional step to send CAE signing certificate to T300
This requires a new permission, available on new product
Transitory solution:
On old T300 in v2.7, upgrade first to v2.8.2, then to v2.9.
On T300 in v2.8 or already upgraded to v2.9, Reset HU250 to default configuration (SecAdmin mode) , then reload T300 configuration
In both cases:
Note that RBAC will be cleared in the process and cybersecurity configuration need to be reloaded
Link copied. Please paste this link to share this article on your social media post.
Difficulty is linked to more security added between CAE and T300, with an additional step to send CAE signing certificate to T300
This requires a new permission, available on new product
Transitory solution:
On old T300 in v2.7, upgrade first to v2.8.2, then to v2.9.
On T300 in v2.8 or already upgraded to v2.9, Reset HU250 to default configuration (SecAdmin mode) , then reload T300 configuration
In both cases:
Note that RBAC will be cleared in the process and cybersecurity configuration need to be reloaded