Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi team,
My customer installed and configured BTA in T300. Now, they want change to Semi -Auto BTA (No Return).
I read Application note and see document mention to No Return ( ATS will be locked) => How do I do setting No Return in BTA.
Thanks very much.
Link copied. Please paste this link to share this article on your social media post.
Hello,
in the list of "parameters" of the ATS_BTA program (Set point list), you will find one called ATS_P_BEHAVIOR.
It has to be set to 1 to activate the No return mode.
Best regards,
Mathieu.
Link copied. Please paste this link to share this article on your social media post.
@Mathieu_Lansoy , could you please help with this technical question. Thanks a lot in advance for your support.
Link copied. Please paste this link to share this article on your social media post.
Hello,
in the list of "parameters" of the ATS_BTA program (Set point list), you will find one called ATS_P_BEHAVIOR.
It has to be set to 1 to activate the No return mode.
Best regards,
Mathieu.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.