Hello
How to implement TCS (Trip coil Supervision) in Easergy P3 Protection Relay?
Best Regard.
Link copied. Please paste this link to share this article on your social media post.
Hello,
This function is described in the manual as per the extract below. It shows how to implement the function and the logic needed
Link copied. Please paste this link to share this article on your social media post.
The user manual for FW30.206 release contains one more TCS principle. This is the combined CB status and TCS inputs. Enclosed the manual text. You can expect these manuals becoming public during week 46 / 2022
Link copied. Please paste this link to share this article on your social media post.
Hello,
This function is described in the manual as per the extract below. It shows how to implement the function and the logic needed
Link copied. Please paste this link to share this article on your social media post.
The user manual for FW30.206 release contains one more TCS principle. This is the combined CB status and TCS inputs. Enclosed the manual text. You can expect these manuals becoming public during week 46 / 2022