PowerLogic T300 - How to set Modbus Master operation?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - How to set Modbus Master operation?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
Windsor
Lt. Commander Windsor Lt. Commander
Lt. Commander

Posted: ‎2022-08-17 10:40 AM . Last Modified: ‎2025-01-24 02:01 AM

0 Likes
2
845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-17 10:40 AM

PowerLogic T300 - How to set Modbus Master operation?

I have a T300 RTU running firmware version 2.8.4 which is talking to a PM8240 meter using Modbus over an RS485 link. The RTU has been configured using Easergy Builder V1.7.9 with the following Modbus master parameters for the meter device:

 

Offline period : 10000 ms

Retries after timeout : 5

Reties after error : 3

 

What I am finding (by examining the Modbus channel trace display in the web server) is that occasionally one of the Modbus replies from the meter has the top bit of the function code byte set to indicate an error and contains an exception code of 2.

 

The trace then shows no further communications to the device until approx 10 seconds have passed (the offline period presumably). 

 

However the trace does not seem to show the retries that should have been performed prior to the backoff period. Is this expected behaviour or am I misunderstanding something?

Labels
  • Labels:
  • PowerLogic T300
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2022-09-02 10:22 AM

0 Likes
1
838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-02 10:22 AM

In this case the exception code 2 means invalid address.

The firmware assumes that this is due to a wrong configuration, so it makes no sense to retry.

 

These are the list of exceptions codes that behave like this.

 

  • ILLEGAL_FUNCTION                0x01  
  • ILLEGAL_DATA_ADDRESS        0x02
  • ILLEGAL_DATA_VALUE              0x03
  • NEGATIVE_ACKNOWLEDGE      0x07

 

Tags (1)
  • Tags:
  • english
Reply
Windsor
Lt. Commander Windsor Lt. Commander
Lt. Commander

Posted: ‎2022-09-04 08:05 AM

0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-04 08:05 AM

Hi @TomBerry,

 

After looking at the exported Modbus channel trace (file attached) again it seems to me that at least 2 reties are taking place before the response containing the exception code is received but there is nothing in the trace to suggest why the retries are occurring.

 

If you have the time to take a quick look it would be much appreciated (the lines of interest in the file have been annotated starting with //)

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of