PowerLogic T300 - How to replace an Easergy PS50 power supply unit?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - How to replace an Easergy PS50 power supply unit?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2024-07-29 04:25 AM . Last Modified: ‎2024-07-31 01:13 AM

0 Likes
4
1506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-29 04:25 AM

PowerLogic T300 - How to replace an Easergy PS50 power supply unit?

Hi team,

 

My customer using T300 with PS50. Now, PS50 was faulty and customer want replacement this PS50.

 

I have a concern

 

- Do i need shutdown electrical before replace.

- Method of Statement.

- Does T300 lost program?

- Any take note for this job replace...

 

Thanks very much.

Labels
  • Labels:
  • PowerLogic T300
Tags (4)
  • Tags:
  • english
  • PowerLogic T300
  • PS50
  • t300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2024-07-31 01:02 AM . Last Modified: ‎2024-07-31 01:06 AM

0 Likes
1
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-31 01:02 AM

Hi,

To add to Raj's answer, please find some more details.

Since T300 RTU configuration is located into PowerLogic HU250 module, you won't lose T300 "programs and settings" when replacing PS50 (except maybe, a few PS50 parameters).

Note: depending on the way T300 is installed in the substation, you may not need to cut the MV and LV power (however it is preferable to have no power on the incoming/ outgoing MV and LV cables). Also it would be a good idea to investigate why the PS50 failed as it is rare: it could be an installation issue - for instance PS50 earth lead is not correctly grounded.

Warning: to perform any maintenance on T300, you are supposed to have attended the relevant PowerLogic T300 training and to have the relevant safety training to your country/ organization. Only certified engineers are allowed to perform such tasks. Please confirm that is the case.
CAUTION: before doing anything, please make sure you are wearing all required protective equipment and that you are not at risk of safety hazard.

A) To dismount the existing PS50 unit:
a) disconnect PS50 battery cable
b) trip the ACB protecting PS50 AC supply input
c) trip all ACB protecting SC150/ SC160/ LV150 voltage measurement inputs
d) disconnect the earth lead from PS50
e) disconnect inter-modules Ethernet jumpers and inter-modules 12 Vdc supply cables
f) disconnect the Modbus RS-485 cable between HU250 and PS50, as well as the 12 Vdc power cables and HU250 DI5 digital input (if connected to PS50 digital output)
g) disconnect any Ethernet cables connected to HU250 Ethernet ports Eth1/ Eth2, and/ or HU250 4G modem 4G/GPS antennas (only if you are using HU50 optional 4G modem)
CAUTION: for safety reasons, DO NOT DISCONNECT SC15/ SC160/ LV150 CT CT cables, except if you can short-circuit the CT cables coming from the CTs or if the MV/LV substation is not powered by MV or LV
h) using a flat screwdriver, dismount HU250 and SC150/ SC160/ LV150 modules from PS50 DIN rail (without disconnecting any CT connection cables on SC150/SC160/LV150).
i) using a flat screwdriver, dismount the PS50 from the cabinet DIN rail

B) To mount a new PS50 unit, do the same steps but reverse:
a) mount the PS50 on the cabinet DIN rail and make sure it is solidly mounted
b) mount HU250 and SC150/ SC160/ LV150 modules from PS50 DIN rail
c) connect any Ethernet cables connected to HU250 Ethernet ports Eth1/ Eth2, and/ or HU250 4G modem 4G/GPS antennas
d) connect the Modbus RS-485 cable between HU250 and PS50, as well as the 12 Vdc power cables and HU250 DI5 digital input
e) connect inter-modules Ethernet jumpers and inter-modules 12 Vdc supply cables
f) close all ACB protecting SC150/ SC160/ LV150 voltage measurement inputs
g) connect the earth lead to PS50
h) close the ACB protecting PS50 AC supply input: T300 should power on
i) connect PS50 battery cable

For more information on T300 modules, please refer to PS50, HU250, SC150, SC160, and LV150 installation guides that you can find in Schneider web repository.

BR - Jean-Yves

See Answer In Context

Reply
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2024-07-31 02:58 AM . Last Modified: ‎2024-07-31 03:00 AM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-31 02:58 AM

Hi again, 

A typical case for a PS50 (or any power supply) to fail is when it is powered from an MV/LV potential transformer connected to two MV phases (e.g., L1 and L2).

The transformer is connected to the ground on the MV side but not on the LV side: so in case of an MV voltage surge, the earth current will flow through the PS50 instead of flowing on the transformer LV earth lead...

To avoid this, you have to connect the transformer LV side to the earth (or typically shunt it to the MV earth cable.

 

BR - Jean-Yves

See Answer In Context

Reply
Replies 4
Rajasekar_Chandrasekar
Ensign Rajasekar_Chandrasekar Ensign
Ensign

Posted: ‎2024-07-30 11:58 PM

0 Likes
0
1455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 11:58 PM

Hello @SESA528  Please shut down only the PS50 supply and ensure the connected battery is also removed from PS50, this will shutdown the T300 system including HU250 and Connected SC/LV Modules.

After this you can go for the replacement of the PS50.

This will not erase the T300 Program,

Make sure the Modbus address is same in the old and new device. I mean the Device ID set using the dial.

BR

Rajasekar

 

Reply
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2024-07-31 01:02 AM . Last Modified: ‎2024-07-31 01:06 AM

0 Likes
1
1453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-31 01:02 AM

Hi,

To add to Raj's answer, please find some more details.

Since T300 RTU configuration is located into PowerLogic HU250 module, you won't lose T300 "programs and settings" when replacing PS50 (except maybe, a few PS50 parameters).

Note: depending on the way T300 is installed in the substation, you may not need to cut the MV and LV power (however it is preferable to have no power on the incoming/ outgoing MV and LV cables). Also it would be a good idea to investigate why the PS50 failed as it is rare: it could be an installation issue - for instance PS50 earth lead is not correctly grounded.

Warning: to perform any maintenance on T300, you are supposed to have attended the relevant PowerLogic T300 training and to have the relevant safety training to your country/ organization. Only certified engineers are allowed to perform such tasks. Please confirm that is the case.
CAUTION: before doing anything, please make sure you are wearing all required protective equipment and that you are not at risk of safety hazard.

A) To dismount the existing PS50 unit:
a) disconnect PS50 battery cable
b) trip the ACB protecting PS50 AC supply input
c) trip all ACB protecting SC150/ SC160/ LV150 voltage measurement inputs
d) disconnect the earth lead from PS50
e) disconnect inter-modules Ethernet jumpers and inter-modules 12 Vdc supply cables
f) disconnect the Modbus RS-485 cable between HU250 and PS50, as well as the 12 Vdc power cables and HU250 DI5 digital input (if connected to PS50 digital output)
g) disconnect any Ethernet cables connected to HU250 Ethernet ports Eth1/ Eth2, and/ or HU250 4G modem 4G/GPS antennas (only if you are using HU50 optional 4G modem)
CAUTION: for safety reasons, DO NOT DISCONNECT SC15/ SC160/ LV150 CT CT cables, except if you can short-circuit the CT cables coming from the CTs or if the MV/LV substation is not powered by MV or LV
h) using a flat screwdriver, dismount HU250 and SC150/ SC160/ LV150 modules from PS50 DIN rail (without disconnecting any CT connection cables on SC150/SC160/LV150).
i) using a flat screwdriver, dismount the PS50 from the cabinet DIN rail

B) To mount a new PS50 unit, do the same steps but reverse:
a) mount the PS50 on the cabinet DIN rail and make sure it is solidly mounted
b) mount HU250 and SC150/ SC160/ LV150 modules from PS50 DIN rail
c) connect any Ethernet cables connected to HU250 Ethernet ports Eth1/ Eth2, and/ or HU250 4G modem 4G/GPS antennas
d) connect the Modbus RS-485 cable between HU250 and PS50, as well as the 12 Vdc power cables and HU250 DI5 digital input
e) connect inter-modules Ethernet jumpers and inter-modules 12 Vdc supply cables
f) close all ACB protecting SC150/ SC160/ LV150 voltage measurement inputs
g) connect the earth lead to PS50
h) close the ACB protecting PS50 AC supply input: T300 should power on
i) connect PS50 battery cable

For more information on T300 modules, please refer to PS50, HU250, SC150, SC160, and LV150 installation guides that you can find in Schneider web repository.

BR - Jean-Yves
Reply
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2024-07-31 02:18 AM

1 Like
0
1409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-31 02:18 AM

Hi @JYPOC  and @Rajasekar_Chandrasekar ,

 

This is answer very detail. Thanks very much for your support.

Reply
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2024-07-31 02:58 AM . Last Modified: ‎2024-07-31 03:00 AM

0 Likes
0
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-31 02:58 AM

Hi again, 

A typical case for a PS50 (or any power supply) to fail is when it is powered from an MV/LV potential transformer connected to two MV phases (e.g., L1 and L2).

The transformer is connected to the ground on the MV side but not on the LV side: so in case of an MV voltage surge, the earth current will flow through the PS50 instead of flowing on the transformer LV earth lead...

To avoid this, you have to connect the transformer LV side to the earth (or typically shunt it to the MV earth cable.

 

BR - Jean-Yves
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore