Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
39
Arun-kumar_PS
Arun-kumar_PS Mentor
33
ComPact NSX
Back to Protection & Control
ChrisMcC
ChrisMcC
Explorer
Posted: ‎2024-07-19 12:12 AM
1930
It is possible to adjust the trip level of the MCCB while live without risk of false trip? Thanks
  • Thumbnail of ComPact NSX
    ComPact NSX
View products (1)
  • Application cases
Replies 6
Gregoire_Brun
Gregoire_Brun Leader
Leader
Posted: ‎2024-07-22 01:58 AM
1840
hello @ChrisMcC
first question is:
Why did you want to change setting?
Because most of them were determined by the global study of the panel and to touch them could reduce some protection levels.
Nevertheless, if it really needed, if you increase values (tripping level) less risk of nuisance tripping (but you reduce your protection level).
If you decrease values of tripping value, it should be possible to pass to the over side of the slide…
So take care of you during this manipulation, use your security equipment for your safety.
Gregoire Brun
Breaker Product Expert
ChrisMcC
ChrisMcC
Explorer
Posted: ‎2024-07-23 12:12 AM
Hi Gregoire, thank you for the reply. The breaker was initially set 400A, it's safe to raise it 630A, all downstream cabling/equipment is rated. It was decided to do this due to some peak loading coming close to 400A. I'd like to do this without taking plant the down (adjusting while still on), my concern is the potential for a false trip while the adjustment is being made.
Chris
Gregoire_Brun
Leader
Posted: ‎2024-07-24 01:41 AM
@ChrisMcC on this case to risk of false tripping, but be carfull to double check size equipment because in many time with compact NSX 630A , inside equipment, some derating need to be apply .
Double check that inside your equipement, enviromental temperature wasn't higher than 40°C.
a setting at 570A should be more secure....
Gregoire Brun
ChrisMcC
ChrisMcC
Explorer
Posted: ‎2024-07-24 01:58 AM
Thanks again Gregoire, is it possible to adjust upwards while live without risk of tripping? I believe it was issue on older breakers.
Chris
Gregoire_Brun
Leader
Posted: ‎2024-07-25 07:02 AM
No problem @ChrisMcC
if you turn normaly the rotary switch , it should be ok. don't turn slowly
br
Gregoire Brun
ChrisMcC
ChrisMcC
Explorer
Posted: ‎2024-07-25 11:08 PM
Thanks, much appreciated