Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

NSX 630N Trip adjustment

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Re: NSX 630N Trip adjustment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
41
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
Start a Topic
ChrisMcC
ChrisMcC
Explorer

Posted: ‎2024-07-19 12:12 AM

0 Likes
6
2001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-19 12:12 AM

NSX 630N Trip adjustment

It is possible to adjust the trip level of the MCCB while live without risk of false trip? Thanks

  • Thumbnail of ComPact NSX
    Schneider Electric
    ComPact NSX
View products (1)
Labels
  • Labels:
  • Application cases
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Gregoire_Brun
Gregoire_Brun Leader
Leader

Posted: ‎2024-07-22 01:58 AM

0 Likes
1
1911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-22 01:58 AM

hello @ChrisMcC 

first question is:

Why did you want to change setting? 

Because most of them were determined by the global study of the panel and to touch them could reduce some protection levels.

Nevertheless, if it really needed, if you increase values (tripping level) less risk of nuisance tripping (but you reduce your protection level).

If you decrease values of tripping value, it should be possible to pass to the over side of the slide…

So take care of you during this manipulation, use your security equipment for your safety.

Gregoire Brun
Breaker Product Expert
Reply
ChrisMcC
ChrisMcC
Explorer

Posted: ‎2024-07-23 12:12 AM

0 Likes
0
1883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-23 12:12 AM

Hi Gregoire, thank you for the reply. The breaker was initially set 400A, it's safe to raise it 630A, all downstream cabling/equipment is rated. It was decided to do this due to some peak loading coming close to 400A. I'd like to do this without taking plant the down (adjusting while still on), my concern is the potential for a false trip while the adjustment is being made. 

 

Thanks

 

Chris

Reply
Gregoire_Brun
Gregoire_Brun Leader
Leader

Posted: ‎2024-07-24 01:41 AM

0 Likes
0
1860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-24 01:41 AM

@ChrisMcC on this case to risk of false tripping, but be carfull to double check size equipment because in many time with compact NSX 630A , inside equipment, some derating need to be apply . 

Double check that inside your equipement, enviromental temperature wasn't higher than 40°C. 

a setting at 570A should be more secure....

Gregoire Brun
Breaker Product Expert
Reply
ChrisMcC
ChrisMcC
Explorer

Posted: ‎2024-07-24 01:58 AM

0 Likes
0
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-24 01:58 AM

Thanks again Gregoire, is it possible to adjust upwards while live without risk of tripping? I believe it was issue on older breakers.

 

Thanks

 

Chris 

Reply
Gregoire_Brun
Gregoire_Brun Leader
Leader

Posted: ‎2024-07-25 07:02 AM

0 Likes
0
1812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-25 07:02 AM

No problem @ChrisMcC 

if you turn normaly the rotary switch , it should be ok. don't turn slowly

br

Gregoire Brun
Breaker Product Expert
Reply
ChrisMcC
ChrisMcC
Explorer

Posted: ‎2024-07-25 11:08 PM

1 Like
0
1790
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-25 11:08 PM

Thanks, much appreciated

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore