hi guys it seems that there is something wrong with the T300 i am using. I can't access it at all, maybe the IP address has changed or something else is wrong. How to factory reset or reset. I searched for the IP address with IP Scanner and Wireshark and did not find it
its not ip 192.168.0.254
Link copied. Please paste this link to share this article on your social media post.
@John_Archer1 Please send a mail to global-na-tech-support@schneider-electric.com we can help you with factory reset
Link copied. Please paste this link to share this article on your social media post.
Hello,
On the T300, there is no reset possible if you can't connect to the product.
It is a security feature, to protect the majority of the installations, whereas a reset would be usefull in a limited number of cases.
If you can't access to the 'LAN' (default 192.168.0.254 or your setting) nor the WAN (default 192.168.1.10 or your setting) nor the Wifi, you can do nothing with the HU250. (same thing if you lose the passwords)
That said, the IP settings, and more generally the configuration, does normally not change spontaneously, and it is important to understand (and share) what could be the cause of the problem (change in configuration, restart, any event ?)
We had for example people trying to set "white list" on both the LAN and WAN in the same time, thus loosing access to the product.
If something is potentially blocking the Ethernet communications, it is important to know.
Any context information around this problem is welcome.
Best regards,
Mathieu.
Link copied. Please paste this link to share this article on your social media post.
Yes, I configured the Whitelist as you said, but I can no longer access it.How do I get back in touch now?
Link copied. Please paste this link to share this article on your social media post.
@John_Archer1 Please send a mail to global-na-tech-support@schneider-electric.com we can help you with factory reset