While selecting the HW & SW configuration in P741 CORTEC- there is a remark while selecting the CSL1, saying as below
"Only P743 can be selected as PU to support advanced Cyber Security with option 'G' " what does this exactly mean. Can anyone throw some light on it, so that pre-sales team can take care of while ordering the same.
If PU P743 is selected without 61850 communication cards, does that mean we must use CSL0 only?
Thanks
Rajasekhar
Link copied. Please paste this link to share this article on your social media post.
Hi @Rajasekhar_A_CRC_Operations_lead
It is not mandatory that P743_CSL1 must be used with P741_CSL1.
P743_CSL0 or P742_CSL0 can be used with P741_CSL1.
The recommendation in the order form is given in a logical point of view, that is to have CSL1 implemented in all the devices in a site.
Link copied. Please paste this link to share this article on your social media post.
Hello @Rajasekhar_A_CRC_Operations_lead
DREB is not available to order in P742. It is available only in P741 and P743.
CSL1 is implemented in the DREB.
So, you can apply only P743 with P741 for CSL1 implementation.
Yes, for all Px4x, CSL0 is only available for the non-61850 protocol option.
Regards,
Arun
Link copied. Please paste this link to share this article on your social media post.
Hi @Rajasekhar_A_CRC_Operations_lead
It is not mandatory that P743_CSL1 must be used with P741_CSL1.
P743_CSL0 or P742_CSL0 can be used with P741_CSL1.
The recommendation in the order form is given in a logical point of view, that is to have CSL1 implemented in all the devices in a site.