PowerLogic T500 - Retrofit from Saitel DP

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T500 - Retrofit from Saitel DP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
JuanRayo
Lieutenant JuanRayo Lieutenant
Lieutenant

Posted: ‎2024-11-28 02:35 AM . Last Modified: ‎2024-12-12 03:58 AM

0 Likes
0
436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-28 02:35 AM

PowerLogic T500 - Retrofit from Saitel DP

This note covers the recommendations and constraints for both:

 

  • Retrofit projects with legacy versions of I/O modules and HU280 CPU.
  • Retrofit projects with latest versions of I/O modules and HU280 CPU.
  • New projects with HU280 CPU and DIET500 modules.
  • Above use cases with external power supplies.

Inputs for this report are the previous studies for:

  • Power consumption of the XS280/SM_SER.
  • PS280/SM_PS40 performance.
  • Viability study of an external power supply to feed a T500 architecture.

 

The new HU280 CPU has a lot of new functionalities, but with the drawback of the power consumption. This fact makes the need of pay special attention on the specific configuration and its power consumption, to be sure that this one falls in the limit of the backplane specification (35 W max) and, eventually, on the capacity of the power supply.

 

Retrofit projects with legacy versions of I/O modules

This paragraph applies to projects equipped with the following modules:

  • SM_DI32 with part number M520xy0002 (from now on, x, y… means the different module versions based on voltage levels or whatever other parameter).
  • SM_DO16R with part number M522xy0002
  • SM_DO32T with part number M522xy0002
  • SM_SER with part number M512000002
  • SM_AI16 with part number M523200002 and revision prior to C0
  • SM_AI8AO4 with part number M525200002 and revision prior to C0
  • SM_PS with part number M515x20002
  • SM_BPX with part number M545x00002
  • SM_CHX with part number M546x00002
  •  

Projects using the modules related above cannot be upgraded with HU280 modules.

At a minimum, SM_BPX or SM_CHX has to be upgraded to the ones with part numbers M518x00002 or M519x00002.

In addition, even upgrading the chassis or backplane, configurations with a 9-slot backplane or 9-slot chassis cannot be upgraded either, although they can be upgraded if they are using a 4-slot backplane (M518400002) or a M519420002 chassis (chassis with a double 4-slot backplane)

This recommendation applies for both, projects using a SM_PS power supply or an external one.

In addition, if the system is powered with an external power supply, this one, apart from fulfilling the requirements in terms of certifications required for these projects, has to use a 1.5 mm2 (AWG 15) wires no longer than 50 cm (20 in) and the power supply has to be configured to deliver 5.65 Vdc in idle state.

 

Retrofit projects with current versions of I/O modules

 This paragraph applies to projects equipped with the following modules:

  • SM_DI32 with part number M58300002
  • SM_DO16R with part number M586xy0002
  • SM_DO32T with part number M580000002
  • SM_SER with part number M581000002
  • SM_AI16 with part number M523200002 and revision after C0
  • SM_AI8AO4 with part number M525200002 and revision after C0
  • SM_PS40 with part number M508x20002
  • SM_BPX with part number M518x00002
  • SM_CHX with part number M519x00002

 

Projects using the above modules allow to upgrade with HU280 CPU, but it is necessary to pay attention in several aspects, one of them is the power supply: If the system is powered with an external power supply, this one, apart from fulfilling the requirements in terms of certifications required for these projects, has to use a 1.5 mm2 (AWG 15) wires no longer than 50 cm (20 in) and the power supply has to be adjusted to deliver 5.65 Vdc in idle state.

Once covered the topic of the external power supply, the remaining considerations apply for both, systems powered with an external power supply or with a SM_PS40.

 

Projects with a 4-slot backplane or a chassis with double 4-slot backplane

There are no additional constraints for these projects: They support the upgrade of the SM_CPU886e CPU(s) (replacement) to the new one HU280.

.

Projects with a 9-slot backplane or a 9-slot chassis

Worst-cases scenarios are set-up with HU280 modules and SM_SER because they are the ones with higher power consumption.

The worst-case scenario is the one with:

  • An external power supply
  • 7 SM_SER
  • 2 HU280

The power consumption of this scenario surpasses the maximum power allowed by the backplane, so this is a non-supported use case.

Another demandant scenario is the following:

  • 1 SM_PS40 power supply
  • 6 SM_SER
  • 2 HU280

The power consumption of this scenario surpasses the maximum power allowed by the backplane as well, so this is a non-supported use case.

The next most demandant scenario (in terms of power consumption) is the following:

  • 2 SM_PS40 power supply
  • 5 SM_SER
  • 2 HU280

The power consumption of this scenario falls into the maximum power allowed by the backplane (actually, reaches the maximum power supply), so this is a supported use case.

Whatever other use case allow the replacement of the existing SM_CPU866e by the new HU280.

Those projects equipped with only one SM_CPU866e CPU allow the upgrade to HU280 with no restriction.

New T500 projects

 

They include projects with HU280 and T500 I/O modules.

 

Because T500 I/O and Saitel DP I/O modules are the same (T500 I/O modules is just a brand labelling of Saitel DP ones), considerations in previous section (“Retrofit projects with current versions of I/O modules”) apply in fully to the new T500 projects.

 

Labels
  • Labels:
  • Application cases
  • PowerLogic T500
  • Saitel range
Tags (3)
  • Tags:
  • english
  • PowerLogic T500
  • Saitel DP
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of