New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Upgrading Saitel DP configuration for PowerLogicT500
Protection & Control
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2024-11-2802:26 AM
Upgrading Saitel DP configuration for PowerLogicT500
This note covers the way to migrate any configuration done with Easergy Builder tool from Saitel DP to T500.
The issues you can face during to process and the way to sort it out.
Export Saitel DP configuration to HU280
First, we must select the desired Saitel DP configuration in Easergy Builder interface and save it in the format that best suits us.
Once the configuration is saved, we must select the RTU HU280 and we must click on “Load a configuration”, we will select the format we chose before and click “Ok”.
Once the configuration is imported successfully and after opening for the first time the following warning message will be shown.
Click “Yes” to continue the process.
Possible Issue nº1: Channels
One of the limitations of this process is the real number of serial ports in DP and HU280.Look at the picture bellow.
If we are using more than 2 COM ports in the channel configuration on the Saitel DP, we will find that when opening the HU280 updated configuration, on the channel, a “INVALID CONFIGURATION” notification will appear. This is because we cannot have more than 2 COM channels in the HU280. To fix this, we just need to open the channel with the error and update it. Note that the expanse module for serial channels was called SM_SER for DP family and now is called XS280.
Possible Issue nº2 : CoreDb Points
To check what exceptions can appear, we will go to the coreDb and click on “CoreDb Checking”, verifying in this way all the points in the coreDb.
WARN_BAT does not exist
We can find that the WARN_BAT point no longer exists. The solution is to eliminate it from the coreDb.
SM_SER not included in the configuration
If the SM_SER supervisión points fail, we will go to the configuration and check that the correct XS280 number is added.
Possible Issue nº3: Ethernet Coordinates
The supervision ethernet coordinates have been modified and when check out the coreDb we will find the following error.
To solve it we will open the wizard for the point creation and select the correct coordinate name.
After that, we will modify the point of selected coordinate name being the final result as follows.
Note : In a redundant configuration the “additional IP´s addresses” , located in « dbRED » tab on Easergy Builder interface, can also be linked to the name of an ethernet interface and therefore with the possibility of being misinterpreted in the new T500 configuration like in the example above once we upgrade a DP config.
Note : In terms of synchronization T500 can also be used as a SNTP or PTP ”Synchronization Server”, located in « Synchronization » tab on Easergy Builder tool interface.
There we can also link this functionality with the name of an ethernet interface and therefore with the possibility of being misinterpreted in the new T500 configuration like in the example above once we upgrade a DP config.
Possible Issue nº4: WebUI differences
As per the webUI, the only differences that we will encounter is that in the configuration menu for the SAITEL DP we will only find the alarm levels menu whilst on the HU280 we will find the new menu for configuring the IHM parameters. More details here in the pictures bellow.