Upgrading Saitel DP configuration for PowerLogicT500

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Upgrading Saitel DP configuration for PowerLogicT500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
JuanRayo
Lieutenant JuanRayo Lieutenant
Lieutenant

Posted: ‎2024-11-28 02:26 AM . Last Modified: ‎2024-12-03 01:26 AM

0 Likes
0
282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-28 02:26 AM

Upgrading Saitel DP configuration for PowerLogicT500

This note covers the way to migrate any configuration done with Easergy Builder tool from Saitel DP to T500.

The issues you can face during to process and the way to sort it out.

Export Saitel DP configuration to HU280

First, we must select the desired Saitel DP configuration in Easergy Builder interface and save it  in the format that best suits us.

 

JuanRayo_0-1732788368257.png

 

Once the configuration is saved, we must select the RTU HU280 and we must click on “Load a configuration”,  we will select the format we chose before and click “Ok”.

 

Once the configuration is imported successfully and after opening for the first time the following warning message will be shown.

 

JuanRayo_1-1732788491654.png

 

Click “Yes” to continue the process.

 

JuanRayo_2-1732788503558.png

    
Possible Issue nº1: Channels

 

One of the limitations of this process is the real number of serial ports in DP and HU280.Look at the picture bellow.

JuanRayo_3-1732788541950.png

If we are using more than 2 COM ports in the channel configuration on the Saitel DP, we will find that when opening the HU280 updated configuration, on the channel, a “INVALID CONFIGURATION” notification will appear. This is because we cannot have more than 2 COM channels in the HU280. To fix this, we just need to open the channel with the error and update it. Note that the expanse module for serial channels was called SM_SER for DP family and now is called XS280.

 

JuanRayo_4-1732788564214.png

 

Possible Issue nº2 : CoreDb Points


To check what exceptions can appear, we will go to the coreDb and click on “CoreDb Checking”, verifying  in this way all the points in the coreDb.

JuanRayo_5-1732788598259.png

 

WARN_BAT does not exist

We can find that the WARN_BAT point no longer exists. The solution is to eliminate it from the coreDb. 

 

JuanRayo_6-1732788749855.png

 

SM_SER not included in the configuration

 

JuanRayo_7-1732788762316.png

 

If the SM_SER supervisión points fail, we will go to the configuration and check that the correct XS280 number is added.

JuanRayo_8-1732788770601.png

Possible Issue nº3: Ethernet Coordinates

  The supervision ethernet coordinates have been modified and when check out the coreDb we will find the following error.

 

JuanRayo_9-1732788891814.png

 

To solve it we will open the wizard for the point creation and select the correct coordinate name.

JuanRayo_10-1732788960684.png

 

After that, we will modify the point of selected coordinate name being the final result as follows.

JuanRayo_11-1732789002557.png

JuanRayo_12-1732789010337.png

 

 

 

Note : In a redundant configuration the “additional IP´s addresses” , located in « dbRED » tab on Easergy Builder interface, can also be linked to the name of an ethernet interface and therefore with the possibility of being misinterpreted in the new T500 configuration like in the example above once we upgrade a DP config.

 

Note : In terms of synchronization T500 can also be used as a SNTP or PTP ”Synchronization Server”, located in « Synchronization » tab on Easergy Builder tool interface.

There we can also link this functionality with the name of an ethernet interface and therefore with the possibility of being misinterpreted in the new T500 configuration like in the example above once we upgrade a DP config.

 

Possible Issue nº4: WebUI differences

 

As per the webUI, the only differences that we will encounter is that in the configuration menu for the SAITEL DP we will only find the alarm levels menu whilst on the HU280 we will find the new menu for configuring the IHM parameters. More details here in the pictures bellow.

 

JuanRayo_14-1732789048708.png

 

 

 

 

 

 

 

Labels
  • Labels:
  • PowerLogic T500
  • Saitel range
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of