PowerLogic T300 - Getting SOE event time and convertin it to Modbus register

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - Getting SOE event time and convertin it to Modbus register
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
23
HenriGRASSET
Captain HenriGRASSET Captain
15
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All
Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Anonymous user
Not applicable

Posted: ‎2020-12-22 12:21 AM . Last Modified: ‎2025-05-26 01:49 AM

0 Likes
2
1073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-22 12:21 AM

PowerLogic T300 - Getting SOE event time and convertin it to Modbus register

May I ask how to get T300 SC150 (CB OPEN/CLOSE, ES OPEN/CLOSE) SOE event TIME and convert to Modbus and assign it to a Modbus Register address?

 

As we need to mapping the CB / ES exact OPEN CLOSE TIME and put it on HMIGTO touch screen and this Touch Screen model only supply Modbus TCP.

 

 

Many thanks.

 

Tony Leung

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • Application cases
  • PowerLogic P3
  • PowerLogic T300
Tags (3)
  • Tags:
  • english
  • PowerLogic T300
  • SOE
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-01-13 07:28 PM . Last Modified: ‎2021-01-13 07:37 PM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-13 07:28 PM

The only reason why the customer do not accept using the smartphone / tablet / embedded windows ..etc... is because those OS will release the latest update service pack OS update every months, and under the customer company policy, they must update it for the security reason, and they are not willing to spend the manpower to do  those update every months since there are 15,000+ substations, so they end up with the Schneider GTO series HMI touchscreen since the GTO do not have the OS update issue but it has very limited function.

 

Correct me if i am wrong that as far as i know Modbus is not a time based protocol that do not have the time stamping on every single TX RX message, only those time stamping data protocol would be supported (IEC104 / DNP3 / IEC61850 /  a proper SCADA on windows... etc).

 

And also the problem of T300 https web console do not have the ability to do the custom HMI design drawing, lets said my architecture has other devices such as protection relay , M580 PLC, ComX510, Power Meters.....and i cannot draw those on https web because there is no such function.

 

So here comes my question was    since I had already collected the real time stamp SOE time on the T300 https EVENT log page,     is there any way to get the value from the event log table and brings the string value to the Modbus as a bit word format to transmit the time log to the HMI through modbusTCP.....but it seems no one would do such custom works to get the value this way, but thanks Jean-Yves and appreciate for your reply.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2021-01-13 01:47 AM . Last Modified: ‎2021-01-13 01:48 AM

0 Likes
1
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-13 01:47 AM

Hi Tony,

 

The only way to reuse the time-stamping data coming from SC150 open/close control & status is to utilize a SCADA protocol that is fitted with time-stamping feature (and Modbus is not one of them: if you have a time-stamping capability then it is not a standard Modbus version but a proprietary one... and there are many of them with no compatibility between them).

 

If you really want to have a permanent HMI attached, the only solution to get the source time-stamping data would be to use a HMI model capable of accessing to T300 embedded webserver through HTTPS, or capable to operate with a standard time-stamped protocol.

 

Can you please describe a bit the architecture and the reason to have a HMI here? Why not use a Smartphone or a tablet to connect in HTTPS via Wifi to the T300 webserver? That would be way more secure than just using Modbus...

 

BR - Jean-Yves
  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (7)
  • Tags:
  • Distribution Automation
  • easergy t300
  • english
  • modbus
  • secondary substation
  • t300
  • time stamping
Reply
Anonymous user
Not applicable

Posted: ‎2021-01-13 07:28 PM . Last Modified: ‎2021-01-13 07:37 PM

0 Likes
0
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-13 07:28 PM

The only reason why the customer do not accept using the smartphone / tablet / embedded windows ..etc... is because those OS will release the latest update service pack OS update every months, and under the customer company policy, they must update it for the security reason, and they are not willing to spend the manpower to do  those update every months since there are 15,000+ substations, so they end up with the Schneider GTO series HMI touchscreen since the GTO do not have the OS update issue but it has very limited function.

 

Correct me if i am wrong that as far as i know Modbus is not a time based protocol that do not have the time stamping on every single TX RX message, only those time stamping data protocol would be supported (IEC104 / DNP3 / IEC61850 /  a proper SCADA on windows... etc).

 

And also the problem of T300 https web console do not have the ability to do the custom HMI design drawing, lets said my architecture has other devices such as protection relay , M580 PLC, ComX510, Power Meters.....and i cannot draw those on https web because there is no such function.

 

So here comes my question was    since I had already collected the real time stamp SOE time on the T300 https EVENT log page,     is there any way to get the value from the event log table and brings the string value to the Modbus as a bit word format to transmit the time log to the HMI through modbusTCP.....but it seems no one would do such custom works to get the value this way, but thanks Jean-Yves and appreciate for your reply.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of