Protection relays and Ethernet/IP protocol

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Protection relays and Ethernet/IP protocol
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Ivan_Puškaš_EC
Lieutenant Ivan_Puškaš_EC
Lieutenant

Posted: ‎2021-01-14 04:20 AM . Last Modified: ‎2023-05-30 10:07 PM

0 Likes
1
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-14 04:20 AM

Protection relays and Ethernet/IP protocol

Hi everyone,

 

We need a Ethernet/IP protocol and IEC61850 protocol on the same protection relay. Difficult part is Ethernet/IP industrial protocol. As far as we know, none SE relays has it these days.

 

Easergy P3 had it few firmware's back but now it seems it is not included any more.

Because of all his other features (differential protection, arc protection,two Ethernet protocols at same time and so on) it is most qualified for the end customers expectations.

 

What now we are not sure:

Is it possible to order old firmware of Easergy P3 relays (one that had Ethernet/IP)?

Is there any other way for P3 to have this protocol?

Is there any other SE relay with this protocol? (Vamp had it but it is obsolete now) 

 

If someone have some information that could help it would be appreciated because we talk about the project with over 100+ relays in the first phase.

 

Also does anyone have suggestion for external protocol  converter (modbus TCP or IEC61850) to  Ethernet/IP? 

 

Best regards,

Labels
  • Labels:
  • PowerLogic P3
  • PowerLogic P5
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
UIRÊ_RIBEIRO
Lieutenant JG UIRÊ_RIBEIRO Lieutenant JG
Lieutenant JG

Posted: ‎2021-01-14 04:32 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-14 04:32 AM

Dear Ivan,

 

Ethernet/IP Protocol on Easergy P3 relays were disabled because of security problems detected on the protocol. As far as I know it is still in the firmware but must be activated throughout scripts which should be asked to the global support. But since there'is this problem, the customer must accept the risks.

Since my information is from a few months ago, I supposed @PekkaHAMALAINEN could confirm this information.

 

About having an alternative within our relays, you could use Easergy P5! I've tested it for applications with IEC61850 and Ethernet/IP here in Brazil and it seems to work perfectly.

 

Best Regards,

See Answer In Context

Tags (4)
  • Tags:
  • Easergy P3
  • easergy p5
  • english
  • Ethernet-IP
Reply
Reply 1
UIRÊ_RIBEIRO
Lieutenant JG UIRÊ_RIBEIRO Lieutenant JG
Lieutenant JG

Posted: ‎2021-01-14 04:32 AM

0 Likes
0
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-14 04:32 AM

Dear Ivan,

 

Ethernet/IP Protocol on Easergy P3 relays were disabled because of security problems detected on the protocol. As far as I know it is still in the firmware but must be activated throughout scripts which should be asked to the global support. But since there'is this problem, the customer must accept the risks.

Since my information is from a few months ago, I supposed @PekkaHAMALAINEN could confirm this information.

 

About having an alternative within our relays, you could use Easergy P5! I've tested it for applications with IEC61850 and Ethernet/IP here in Brazil and it seems to work perfectly.

 

Best Regards,

Tags (4)
  • Tags:
  • Easergy P3
  • easergy p5
  • english
  • Ethernet-IP
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore