Protection & Control
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi,
There is no software which converts CID to SCD. To just change the file name into *.SCD is no good.
Since the SCADA software expects System Configuration Descriptions (SCD), you have to provide this type of configuration file to SCADA. The IED which you are talking of is a part of a system which should have been configured from an SCD. So you need to update the project SCD with the latest IED configuration.
If you read out the IEC 61850 configuration from the IED, then you used a tool to do this: the IED Configuration Tool (ICT). This tool is also in charge of creating Instantiated IED Descriptions (IID) of the IED configurations.
The System Configuration Tool (SCT) which created the SCD is able to import IID. Using the IID you update the project system database and you create a new SCD. This is the file to provide to SCADA.
Best regards
Link copied. Please paste this link to share this article on your social media post.
Hello There,
Try change the extension of the file. It's should be enough
Link copied. Please paste this link to share this article on your social media post.
Please tell me know what software can do that?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi,
There is no software which converts CID to SCD. To just change the file name into *.SCD is no good.
Since the SCADA software expects System Configuration Descriptions (SCD), you have to provide this type of configuration file to SCADA. The IED which you are talking of is a part of a system which should have been configured from an SCD. So you need to update the project SCD with the latest IED configuration.
If you read out the IEC 61850 configuration from the IED, then you used a tool to do this: the IED Configuration Tool (ICT). This tool is also in charge of creating Instantiated IED Descriptions (IID) of the IED configurations.
The System Configuration Tool (SCT) which created the SCD is able to import IID. Using the IID you update the project system database and you create a new SCD. This is the file to provide to SCADA.
Best regards
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.