Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerLogic T300 - Connection no longer possible (webserver, Easergy Builder)

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - Connection no longer possible (webserver, Easergy Builder)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
41
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
pradiptasetio
pradiptasetio
Contributor

Posted: ‎2020-11-15 11:31 PM . Last Modified: ‎2025-05-27 06:37 AM

0 Likes
1
1734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-15 11:31 PM

PowerLogic T300 - Connection no longer possible (webserver, Easergy Builder)

Hi,

 

I was trying to setup communication between CitectSCADA and PowerLogic T300 (formerly named Easergy T300) and modifying the RTU DNP3 slave settings a few times and then, suddenly, I could no longer establish a connection from Easergy Builder.

I tried to login to the web page but none of the username worked. I had tried all the usernames from Installer to SecurityAdmin but to no avail (bad username and password)

 

Does anyone know why this happen and how do I login again to the RTU?

 

Note: I haven't tried to access the T300 again since then because it's located in customer's workshop.

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (5)
  • Tags:
  • Distribution Automation
  • easergy t300
  • english
  • logging
  • PowerLogic T300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2021-01-13 01:00 AM . Last Modified: ‎2021-01-13 01:03 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-13 01:00 AM

Hi,

 

The issue you mention has been reported in 2016 on Easergy T300 old firmware versions up to V1.2.1, and was solved with the launch of V1.2.2 firmware in Feb 2017 (which means this T300 unit has not been updated for almost 4 years!).

 

As a reminder, every year we launch a new Easergy T300 firmware version to provide new features and to answer cybersecurity evolving requirements: in Q2/2020, we launched V2.7.1 which is a signed firmware (see release note to find more details) and we recommend that all T300 units are updated with this version.

 

Now regarding the specific issue, please contact global-na-tech-support@schneider-electric.com to see what to do (you will need to recover the equipment from the customer and perform the operation in a Schneider Electric facility).

 

Regards,

BR - Jean-Yves

See Answer In Context

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (5)
  • Tags:
  • cybersecurity
  • Distribution Automation
  • easergy t300
  • english
  • logging
Reply
Reply 1
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2021-01-13 01:00 AM . Last Modified: ‎2021-01-13 01:03 AM

0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-13 01:00 AM

Hi,

 

The issue you mention has been reported in 2016 on Easergy T300 old firmware versions up to V1.2.1, and was solved with the launch of V1.2.2 firmware in Feb 2017 (which means this T300 unit has not been updated for almost 4 years!).

 

As a reminder, every year we launch a new Easergy T300 firmware version to provide new features and to answer cybersecurity evolving requirements: in Q2/2020, we launched V2.7.1 which is a signed firmware (see release note to find more details) and we recommend that all T300 units are updated with this version.

 

Now regarding the specific issue, please contact global-na-tech-support@schneider-electric.com to see what to do (you will need to recover the equipment from the customer and perform the operation in a Schneider Electric facility).

 

Regards,

BR - Jean-Yves
  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (5)
  • Tags:
  • cybersecurity
  • Distribution Automation
  • easergy t300
  • english
  • logging
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore