PowerLogic T300 - Clock synchronization of IEDs on the internal LAN port?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - Clock synchronization of IEDs on the internal LAN port?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All
Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2023-07-24 03:43 AM . Last Modified: ‎2025-01-24 01:00 AM

0 Likes
3
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-24 03:43 AM

PowerLogic T300 - Clock synchronization of IEDs on the internal LAN port?

Dear all,

 

I have a question regarding the possibily to use PowerLogic T300 to synchronize the clock of local IEDs.

After configurating the IP address of an IED as 192.168.0.4 and the SNTP server as 192.168.0.254, I connect the IED to the second Ethernet LAN port of the 3rd SC150 module (the last module of my T300 hardware configuration). It synchronized but then it losts communication over IEC61850.

 

My questions are:

  1. Do I need to configure an IP address of IED to be in the same range as LAN port, or could the IP address be from a different range?
  2. On which Eternet port do I need to connect the IED (LAN or WAN)?
  3. What else needs to be set up?

 

Thanks in advance.

 

Best regards,
Milica Dukic

 

 

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • IEC61850
  • PowerLogic T300
Tags (4)
  • Tags:
  • english
  • PowerLogic T300
  • sntp
  • t300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2023-07-25 12:34 AM . Last Modified: ‎2025-01-24 01:20 AM

0 Likes
1
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-25 12:34 AM

IEDs should be connected to the ETH1 WAN port of the HU250 module (and not to SC150, SC160 or LV150 modules).

Then the IED should be configured to get time synchronization from a router, or via SNTP from the HU250 module using HU250's WAN IP address.

 

HU250 LAN port (subnetwork 192.168.0.x) is strictly reserved for internal communications with SC150, SC160 and LV150 modules (see T300 user manual page 26 - chapter: "T300 Internal Architecture")

See Answer In Context

Reply
Replies 3
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2023-07-25 12:34 AM . Last Modified: ‎2025-01-24 01:20 AM

0 Likes
1
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-25 12:34 AM

IEDs should be connected to the ETH1 WAN port of the HU250 module (and not to SC150, SC160 or LV150 modules).

Then the IED should be configured to get time synchronization from a router, or via SNTP from the HU250 module using HU250's WAN IP address.

 

HU250 LAN port (subnetwork 192.168.0.x) is strictly reserved for internal communications with SC150, SC160 and LV150 modules (see T300 user manual page 26 - chapter: "T300 Internal Architecture")

Reply
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2023-07-26 06:01 AM

0 Likes
0
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-26 06:01 AM

Thanks Tom.

 

Best regards, Milica

Reply
John_Archer1
Ensign John_Archer1
Ensign

Posted: ‎2024-10-28 03:16 AM

0 Likes
0
555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-28 03:16 AM

Hello Tomberry, I can't adjust the time of the computer that is monitoring the scada system using the NTP protocol of the T300. Please let me know about this.

T300 Can a normal computer be set to synchronous time?
SCADA is able to adjust the timing of other relays connected to the system.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of