Hi all,
Anyone encounter something like described below with Micom P437 ver. -660 (PX437-660-252ED1.ICD version)
We have: SEB copper: 1 * RJ45 + 1 * IRIG-B (9652161)
We cant ping the device even we changed the IP address in MCL, and downloaded MCL. More we are pinging IP address: 192.168.1.4
Any one know what we are doing wrong or this can be the bug in Micom -660?
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Hi Ivan,
Unfortunately, 660 version can not used in Edition 1 mode.
If you can run Edition 2 in the substation, then you can use the P437 with version 660.
Switch over to Edition 2 mode by using the setting tool Easergy Studio.
If Edition 1 is mandatory for P437, then an update to at least version 661-706 is required.
Best regards,
Johannes
Link copied. Please paste this link to share this article on your social media post.
Hi Ivan,
Unfortunately, 660 version can not used in Edition 1 mode.
If you can run Edition 2 in the substation, then you can use the P437 with version 660.
Switch over to Edition 2 mode by using the setting tool Easergy Studio.
If Edition 1 is mandatory for P437, then an update to at least version 661-706 is required.
Best regards,
Johannes