Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Easergy measurement with Phase rotation Enabled

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy measurement with Phase rotation Enabled
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
60
Arun-kumar_PS
Arun-kumar_PS Mentor
26
JuanRayo
JuanRayo Mentor
24
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic P2

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
Start a Topic
sesa158822_brid
sesa158822_brid Contributor
Contributor

Posted: ‎2023-03-13 07:39 AM . Last Modified: ‎2023-05-30 10:07 PM

0 Likes
2
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-13 07:39 AM

Easergy measurement with Phase rotation Enabled

Dear community

I need some guidence on resolving an issue :
We are using Easergy P3 with 2LL+VN/LLY  voltage mode in the "ACB" reverse rotation system,
Since Easergy relay is swapping readings of Phase "B" and "C" ( Voltage and Current ) to adopt the mesurement with ACB system,
this is causing issue and wrong measurement with 2LL+VN/LLY mode.
We  ended up to change relay connection to have correct reading on synch voltage.
Now current angle are not read correctly.....
I compared it with MiCOM P145, 
P145 reading is correct under both ABC and ACB system , and sequence components are also read correctly.

Appreciate your comments.

Regards

  • Thumbnail of PowerLogic P2
    PowerLogic
    PowerLogic P2
View products (1)
Labels
  • Labels:
  • PowerLogic P5
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Juha
Juha Leader
Leader

Posted: ‎2023-03-16 04:06 AM

0 Likes
0
1397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-16 04:06 AM

Hi @sesa158822_brid, the relay is measuring exactly what in injected to the relay. The realy can't possibly know which way the network is rotating but it is all about how the wiring is done. I always say that there is no absolute reference available for angles. 

 

Now, for ABC rotation, the wiring of the relay for 2LL+U0/LLy measurement mode is such that the relay is 
measuring UAB and UBC. For synchrochekc UAB is measured. 
For ACB rotation relay is wired as follows then: UAC, UCB and UAC for synchrocheck.
Let me add here a simple sketch of the wiring.

Capture.JPG

 

 

 

BR

 

-juha-

Reply
sesa158822_brid
sesa158822_brid Contributor
Contributor

Posted: ‎2023-03-16 07:50 AM

0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-16 07:50 AM

Hi Juha
Thanks for eplay
few points:
when we set the relay with " Enable phase rotation" what relay will do?
it suppose to overcome the phase rotation and compensate it.
but what it is doing , it is simply swapping reding of Phase "B" and "C" 
means if we inject to phase "B" of the relay, it will be seen as pghase "C" current and vise versa.
So based on your comment , first we need to figure out which phase have been swapped and then change the connection accordingly? then ACB and CBA rotation will need different connections.

 

Thanks for your comment

Rgards
Farhad

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.