Hi Ivan, Unfortunately, 660 version can not used in Edition 1 mode. If you can run Edition 2 in the substation, then you can use the P437 with version 660. Switch over to Edition 2 mode by using the setting tool Easergy Studio.
If Edition 1 is mandatory for P437, then an update to at least version 661-706 is required.