Easergy T300: can it be configured for 19 SC150 and 4 LV150 modules?
Hello everyone,
How many modules (SC150, LV150) can support HU250 module, if not powered from PS module? I've came across different information considering this topic.
Specifically, I'm interested if it's possible for Easergy T300 to have this configuration: HU250, 19xSC150, 4xLV150? Is this too many modules for HU250 to support?
Thanks in advance.
- Labels:
-
PowerLogic T300
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello,
Easergy T300 can be set-up with up to 23 SC150 modules, and up to 6 LV150.
So 19*SC150 +4*LV150 is possible.
With such a large configuration, PM and PQ options should not be activated if not necessary.
Mathieu.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
HI,
Agreed with Mathieu about to avoid unnecessary configuration, remember that the T300 modules like SC150 uses an 104 channel through a ethernet daisy chain to communicate with the Head Unit. So it is a good practice to optimize the dataflow as much as possible.
BR