Easergy T300: antenna for 4G modem

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy T300: antenna for 4G modem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2021-02-10 04:22 AM . Last Modified: ‎2023-05-30 09:57 PM

0 Likes
2
572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-10 04:22 AM

Easergy T300: antenna for 4G modem

Hello everyone,

 

In one project with Easergy T300 we have 4G modem (HU250 – 4G – GPS) as GPS synchronization device. We have a small antenna which came with modem. Is this antenna enough or we need additional?
If it is necessary do we need a SE antenna (EMS59161) or we can use some third party antenna? Which model and which characteristics that model of antenna need to have?

 

Thanks in advance,

 

Milica Dukić

Labels
  • Labels:
  • PowerLogic T300
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-02-17 01:04 AM

0 Likes
1
559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-17 01:04 AM

Hello Milica,

yes, that's correct, you absolutely need 2 different antennas, one used for the GPS synchro and the other one for the 3G or 4G cellular data. 

EMS59161 must be connected to the upper connector of HU250 for the GPS synchronization and has to be localized outdoor, with a direct view to the sky... and eventually a  3rd party antenna should make the job if it is dedicated for that frequency : 1575 MHz.

 

One important point, in case you are using cellular data, it's recommended also using the outdoor antenna (EMS59160) connected to the lower connector of HU250. In this case, it is possible also to synchronize the T300 with this antenna, using a SNTP server available inside your cellular network, if any. This synchronisation, using the cellular data is less accurate than using the GPS antenna which provide a 1 ms time synchronisation accuracy. 

BR

Yves Chollot

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Anonymous user
Not applicable

Posted: ‎2021-02-17 01:04 AM

0 Likes
1
560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-17 01:04 AM

Hello Milica,

yes, that's correct, you absolutely need 2 different antennas, one used for the GPS synchro and the other one for the 3G or 4G cellular data. 

EMS59161 must be connected to the upper connector of HU250 for the GPS synchronization and has to be localized outdoor, with a direct view to the sky... and eventually a  3rd party antenna should make the job if it is dedicated for that frequency : 1575 MHz.

 

One important point, in case you are using cellular data, it's recommended also using the outdoor antenna (EMS59160) connected to the lower connector of HU250. In this case, it is possible also to synchronize the T300 with this antenna, using a SNTP server available inside your cellular network, if any. This synchronisation, using the cellular data is less accurate than using the GPS antenna which provide a 1 ms time synchronisation accuracy. 

BR

Yves Chollot

Tags (1)
  • Tags:
  • english
Reply
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2021-02-19 05:05 AM

0 Likes
0
554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-19 05:05 AM

@Anonymous user thank you for help.


Best regards,
Milica Dukić

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of