Easergy P5F30 - Underfrequency ANSI81 and ANSI81U / Operation delay

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy P5F30 - Underfrequency ANSI81 and ANSI81U / Operation delay
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic P3

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
PaterninaEnriqu
Ensign PaterninaEnriqu Ensign
Ensign

Posted: ‎2021-01-27 04:55 PM . Last Modified: ‎2023-05-30 10:07 PM

0 Likes
2
1388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-27 04:55 PM

Easergy P5F30 - Underfrequency ANSI81 and ANSI81U / Operation delay

Good morning.

 

I am participating in a project of two (2) bays of 69kV lines + one (1) transformer bay + eight (8) 11.4kV switchgears with Easergy P5 and P3 devices.

 

In this project, specifically for switchgears, I am running routine tests on an Easergy P5F30

 

Order Code P5F30-EECB-GADDH-AAAI
Firmware V01
Build version: 300.103

 

For functions f> </f> <> </ f </ f << I am testing the following settings:

 

fn:60Hz

Un:69kV

TT´s= 69kV/115sqrt(3)

Stage Pick-up value [Hz] Operation delay [s]
1 59.4 0.2
2 59.2 0.2
3 59 0.4
4 58.8 0.4
5 58.6 0.6
6 58.6 1

 

For the test I am sensing two output contacts associated with trip coils 1 and 2. Since I do not have a test case with an advanced module with which I can sense starts and trips via 61850, I support myself by programming a contact associated with the start of the function and downloading the disturbance record (DR).

 

Issue:

For all scenarios, it is not respecting the Operation delay, subtracting the set intentional delay, approximately between 70-80ms. (81U Stage 6 58.6 - 1s CMC256.png and 81U Stage 1 58.4 - 0.2s CMC256.png)

 

Question:

Should I take the "Star Time" described in the manual to defend this behavior to the customer?

 
 

 

Since I have tried devices from other manufacturers and the "Delay Time" is respected, adjusted both in 61850 and the physical sensing of the contacts, taking into account the operating times of these between 5-12ms (for fast and normal contacts).

 

 

Best regards.

  • Thumbnail of PowerLogic P3
    PowerLogic
    PowerLogic P3
View products (1)
Attachments
Labels
  • Labels:
  • Application cases
  • PowerLogic P5
Tags (5)
  • Tags:
  • 81U
  • easergy p5
  • english
  • Operate delay
  • P5
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jinlei_Xing
Commander Jinlei_Xing Commander
Commander

Posted: ‎2021-02-16 05:51 PM

0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-16 05:51 PM

Hi Enrique,

 

Sorry for the late replies.

 

Currently in P5 relay, the setting "Operation delay" means the interval between the "fault inception" and the "relay trip". Your test measured the interval between "relay start" and “relay trip“.  So the "Start time" should be considered when you check the test results with the "Operation delay" setting. The typical "Start time" 80ms is applied to compensate the real time delay between "relay start" and "relay trip". So for setting Operation delay as 200ms, the practical timer is only 120ms  = 200ms - 80ms. 

 

P3 has the similar operation delay philosophy as P5. However, from P5 wave 4 release, such operation delay philosophy will be changed to a more conventional way as your test. The operation time delay setting means the interval between "start" and "trip".

 

 

 

BR,

Jinlei XING

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
PaterninaEnriqu
Ensign PaterninaEnriqu Ensign
Ensign

Posted: ‎2021-01-27 05:08 PM

0 Likes
1
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-27 05:08 PM

Question:

Should I take the "Star Time" described in the manual to defend this behavior to the customer?

 

image.png

Tags (1)
  • Tags:
  • english
Reply
Jinlei_Xing
Commander Jinlei_Xing Commander
Commander

Posted: ‎2021-02-16 05:51 PM

0 Likes
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-16 05:51 PM

Hi Enrique,

 

Sorry for the late replies.

 

Currently in P5 relay, the setting "Operation delay" means the interval between the "fault inception" and the "relay trip". Your test measured the interval between "relay start" and “relay trip“.  So the "Start time" should be considered when you check the test results with the "Operation delay" setting. The typical "Start time" 80ms is applied to compensate the real time delay between "relay start" and "relay trip". So for setting Operation delay as 200ms, the practical timer is only 120ms  = 200ms - 80ms. 

 

P3 has the similar operation delay philosophy as P5. However, from P5 wave 4 release, such operation delay philosophy will be changed to a more conventional way as your test. The operation time delay setting means the interval between "start" and "trip".

 

 

 

BR,

Jinlei XING

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.