Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SAITEL - redundant power supply

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • SAITEL - redundant power supply
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
39
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
milica_dukic_
milica_dukic_
Explorer

Posted: ‎2021-01-18 05:19 AM . Last Modified: ‎2023-05-30 10:09 PM

0 Likes
5
2521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-18 05:19 AM

SAITEL - redundant power supply

Hello everyone,

In one SAITEL project, we need a redundant power supply. What we should know is whether there is a possibility to have different SM_PS40 on the same panel? For example, what we need is 110VDC as main and 230VAC as redundant backup power supply. Is it possible to have SM_PS40/A4 and SM_PS40/A5 on one SAITEL with one CPU module?

If we are correct, SM_PS40/A5 is module for 110/230VAC?

 

Thanks in advance.

Labels
  • Labels:
  • Saitel range
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Iván_González
Iván_González Mentor
Mentor

Posted: ‎2021-01-18 06:28 AM

1 Like
4
2517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-18 06:28 AM

Hi @milica_dukic_ 

 

Your proposal is perfectly feasible. Saitel DP backplanes can host 2 power supplies, each powered from a different voltage source.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
Iván_González
Iván_González Mentor
Mentor

Posted: ‎2021-01-18 06:28 AM

1 Like
4
2518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-18 06:28 AM

Hi @milica_dukic_ 

 

Your proposal is perfectly feasible. Saitel DP backplanes can host 2 power supplies, each powered from a different voltage source.

Tags (1)
  • Tags:
  • english
Reply
Amr_Hesham
Amr_Hesham Explorer
Explorer

Posted: ‎2021-01-19 04:27 AM

0 Likes
2
2509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-19 04:27 AM

Can I have redundant power supply for Saitel DR?

Tags (2)
  • Tags:
  • english
  • Saitel DR
Reply
Iván_González
Iván_González Mentor
Mentor

Posted: ‎2021-01-19 05:46 AM

0 Likes
1
2505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-19 05:46 AM

Hi @Amr_Hesham!

 

Saitel DR does not support redundant supplies. For that type of requirement we can comply using Saitel DP.

Tags (1)
  • Tags:
  • english
Reply
Amr_Hesham
Amr_Hesham Explorer
Explorer

Posted: ‎2021-01-29 06:03 AM

0 Likes
0
2493
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-29 06:03 AM

Thanks @Iván_González 

Tags (1)
  • Tags:
  • english
Reply
milica_dukic_
milica_dukic_
Explorer

Posted: ‎2021-01-31 11:23 PM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-01-31 11:23 PM

Thank you @Iván_González 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore