Dear All ,
One of our Smart RM6 customers would like to share the existing LPVT voltage sensors (going to Easergy SC150 module) with a Revenue Meter. Is that possible and if yes, how?
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Hi @sesa122761_brid ,
LPIT's (Low Power Instrumentation Transformers) can not be paralleled like
traditional instrumentation transformer. It requires an amplifier to distribute the
LPIT signal for several devices.
BR
-juha-
Link copied. Please paste this link to share this article on your social media post.
Hi,
We investigated a few years ago and it was deemed possible to connect up to 3 or 4 Easergy SC150-VT/LPVT modules to a single LPVT output. However, this has not been tested with other products: hence the solution provided (i.e. to use a LPVT sharing hub) will probably be needed to add this revenue meter.
Note: the RM6 is fitted with 3 LPVTs (Class 0.5) and 3 RM6 bushing CTs (Class 0.5). This is why the Easergy T300 provides a Power Measurement at Class 1.
If the revenue meter is connected to the same current/voltage sources, it cannot provide a Power Measurement better than Class1: so what is the idea here???
Link copied. Please paste this link to share this article on your social media post.
Thank you very much.
Do we know the type of 'LPVT sharing hub' in the market that could be used in this case ?
It looks to me any case with the existing LPVT type we use in RM6 , it is not possible to use external additional revenue meter beside SC150 since the accuracy for the meter will not be achieved except customer accepts with some tolerance on the accuracy for the meter ?
Link copied. Please paste this link to share this article on your social media post.
And as I said before, a Revenue Meter can provide a high accuracy on the complete chain when it is directly connected to the voltage (which is the case for LV measurement) and CTs with a Class better than 0.5. . But it won't be the case here as LPVT is Class 0.5 and RM6 bushing CT is Class 0.5.