Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Link copied. Please paste this link to share this article on your social media post.
Dear all,
Does someone has information considering what is voltage treshold for digital inputs on SC150 module? Can it be 110Vdc? I can't find this information in the user manual.
Also, can SC150 module be used to command circuit breaker, which motor pack power supply is 110Vdc?
I would appreciate any information considering this topic.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Hi,
You have installation guide for each module, attached the SC150.
Do not feed any voltage to T300 inputs, you will use dry contacts, i.e. they are wetted inputs.
Link copied. Please paste this link to share this article on your social media post.
@JYPOC @jean-luc_batard @Paco , could any of your reply to this technical question about T300?.
Thanks and Best Regards,
Araceli Monje.
Link copied. Please paste this link to share this article on your social media post.
Hello,
As you have not described T300 hardware architecture, please confirm that you have:
If this information is correct then here are my comments:
If, for historical reasons, an MV switchgear requiring a 110 Vdc power supply has been installed in a typical secondary MV/LV substation (so fitted with 220 Vac power source but no 110 Vdc source), there are two options: