PowerLogic T300 - How to set the ATS-BTA in semi-automatic mode

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - How to set the ATS-BTA in semi-automatic mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
26
HenriGRASSET
Captain HenriGRASSET Captain
15
Arun-kumar_PS
Lt. Commander Arun-kumar_PS Lt. Commander
14
View All
Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2022-11-07 08:23 AM . Last Modified: ‎2025-05-26 12:34 AM

0 Likes
4
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-07 08:23 AM

PowerLogic T300 - How to set the ATS-BTA in semi-automatic mode

Hi team,

 

My customer installed and configured BTA in T300. Now, they want change to Semi -Auto BTA (No Return).

 

I read Application note and see document mention to No Return ( ATS will be locked) => How do I do setting No Return in BTA.

 

Thanks very much.

 

Return.PNG

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (5)
  • Tags:
  • BTA auto transfer source
  • english
  • T300 ATS
  • T300 BTA
  • T300 bus tie automatism
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mathieu_Lansoy
Lt. Commander Mathieu_Lansoy Lt. Commander
Lt. Commander

Posted: ‎2022-11-08 04:45 AM . Last Modified: ‎2022-11-09 01:47 AM

0 Likes
1
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-08 04:45 AM

Hello,

 

in the list of "parameters" of the ATS_BTA program (Set point list), you will find one called ATS_P_BEHAVIOR.

It has to be set to 1 to activate the No return mode.

 

image.png

 

Best regards,

 

    Mathieu.

 

See Answer In Context

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (3)
  • Tags:
  • BTA auto transfer source
  • english
  • T300 ATS
Reply
Replies 4
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
Lt. Commander

Posted: ‎2022-11-08 12:55 AM . Last Modified: ‎2022-11-09 01:49 AM

0 Likes
1
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-08 12:55 AM

@Mathieu_Lansoy , could you please help with this technical question. Thanks a lot in advance for your support.

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (6)
  • Tags:
  • BTA
  • bus tie automatism
  • easergy t300
  • english
  • MV BTA
  • t300
Reply
Mathieu_Lansoy
Lt. Commander Mathieu_Lansoy Lt. Commander
Lt. Commander

Posted: ‎2022-11-08 04:45 AM . Last Modified: ‎2022-11-09 01:47 AM

0 Likes
1
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-08 04:45 AM

Hello,

 

in the list of "parameters" of the ATS_BTA program (Set point list), you will find one called ATS_P_BEHAVIOR.

It has to be set to 1 to activate the No return mode.

 

image.png

 

Best regards,

 

    Mathieu.

 

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (3)
  • Tags:
  • BTA auto transfer source
  • english
  • T300 ATS
Reply
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2022-11-08 10:00 AM . Last Modified: ‎2022-11-09 01:48 AM

0 Likes
0
1304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-08 10:00 AM

Hi @Mathieu_Lansoy ,

 

Great. This is helpful information. Thanks very much.

 

 

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (6)
  • Tags:
  • BTA
  • bus tie automatism
  • easergy t300
  • english
  • MV BTA
  • t300
Reply
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2022-11-09 09:01 AM

0 Likes
0
1293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 09:01 AM

Hi @Araceli_Monje ,

 

Thanks for your support

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of