Hi team,
My customer installed and configured BTA in T300. Now, they want change to Semi -Auto BTA (No Return).
I read Application note and see document mention to No Return ( ATS will be locked) => How do I do setting No Return in BTA.
Thanks very much.
Link copied. Please paste this link to share this article on your social media post.
Hello,
in the list of "parameters" of the ATS_BTA program (Set point list), you will find one called ATS_P_BEHAVIOR.
It has to be set to 1 to activate the No return mode.
Best regards,
Mathieu.
Link copied. Please paste this link to share this article on your social media post.
@Mathieu_Lansoy , could you please help with this technical question. Thanks a lot in advance for your support.
Link copied. Please paste this link to share this article on your social media post.
Hello,
in the list of "parameters" of the ATS_BTA program (Set point list), you will find one called ATS_P_BEHAVIOR.
It has to be set to 1 to activate the No return mode.
Best regards,
Mathieu.