Easergy T300 Configuration Error
Hi, I am trying to configure a T300 RTU but an error occurs.
The message in the RTU syslog file is shown in the attached image.
Is there anyway to get any more information about what is wrong?
The configuration is based on one that does download and all coreDB checks are successful.
- Labels:
-
PowerLogic T300
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
As this is a message for the HU250, scroll down from this message to see the real reason.
When you load a configuration the RTU stopes the main application process and then attempts to restart with the new configuration. If it finds a problem then it will log one or more error messages and then reboot with the original configuration.