SAITEL DP - How to set up redundant SCADA servers?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • SAITEL DP - How to set up redundant SCADA servers?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2020-09-29 06:07 AM . Last Modified: ‎2024-07-05 01:16 AM

0 Likes
4
1830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-29 06:07 AM

SAITEL DP - How to set up redundant SCADA servers?

Hello everyone,

 

In SAITEL project, we have a two redundant SCADA servers with following IP addresses : 10.2.201.10 and 10.2.201.11 (redundant). Physically this is one FO link. When the primary communication is broken, the SAITEL has to communicate with redundant server. Both servers never run at the same time. Is this a way (attached picture Saitel) how we can get this? Just put two addresses in Channel Setup/Channel/Remote IP List? Or is there more to it?

Thanks in advance.

Attachments
Labels
  • Labels:
  • Saitel range
Tags (2)
  • Tags:
  • english
  • Saitel DP
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Iván_González
Lieutenant Iván_González Lieutenant
Lieutenant

Posted: ‎2020-09-30 04:03 AM

1 Like
3
1822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-30 04:03 AM

Hi Milica,

 

It's mostly OK as you show in your picture. However some important remarks to be considered though:

  • The channel should be defined as "CALLED" since we are an IEC104 slave, not master.
  • Events already sent to a SCADA server will not be sent to the backjup one if there's a switchover.
  • This will only work well if we are sure that only one SCADA will be communicating at any given time. If that's not the case, the CPU will always engage with the last SCADA to send a request (and disconnect from the other one).

See Answer In Context

Tags (3)
  • Tags:
  • Easergy Builder
  • english
  • Saitel DP
Reply
Replies 4
Iván_González
Lieutenant Iván_González Lieutenant
Lieutenant

Posted: ‎2020-09-30 04:03 AM

1 Like
3
1823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-30 04:03 AM

Hi Milica,

 

It's mostly OK as you show in your picture. However some important remarks to be considered though:

  • The channel should be defined as "CALLED" since we are an IEC104 slave, not master.
  • Events already sent to a SCADA server will not be sent to the backjup one if there's a switchover.
  • This will only work well if we are sure that only one SCADA will be communicating at any given time. If that's not the case, the CPU will always engage with the last SCADA to send a request (and disconnect from the other one).
Tags (3)
  • Tags:
  • Easergy Builder
  • english
  • Saitel DP
Reply
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2020-10-05 12:19 AM

0 Likes
0
1807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-05 12:19 AM

@Iván_González thank you for the answer.

Regards, 
Milica Dukic

Tags (1)
  • Tags:
  • english
Reply
ZakariaRh
Crewman ZakariaRh Crewman
Crewman

Posted: ‎2021-11-04 02:05 AM

0 Likes
1
1774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-04 02:05 AM

Hi Iván! 

I would like to ask you a question about Saitel too. 

In one of my projects, Saitel is supposed to communicate with two servers, one for a Building Management System, and the second for an Energy Managements System. 
I keep getting communication errors in the BMS Server. the EMS works fine 
From your answer I first recognized that the Saitel is not multimaster capable. 
Did I got it right? 

Thank you! 

Tags (1)
  • Tags:
  • english
Reply
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2021-11-04 04:22 AM

0 Likes
0
1767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-04 04:22 AM

HI @ZakariaRh 

 

SAITEL is multimaster, in your case, you must configure 2 different TCP ports, but it is a TCP thing.

 

Best Regards

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore