Good morning.
I am writing to detail a problem that is happening to us with the Easergy P5F30 that we have mounted in SAT tests for some 69kV line boards integrated into IHM Ecosui.
Problem description
Loss of connection with Easergy Setup via Ethernet and via USB (front panel). The equipment does not allow management through any of its ports. It only allows a temporary connection with the Easergy P5F30 in both ports for about 5-7 min after restarting the equipment (turning off and power on the power supply).
Observations
Procedures performed by on-site technician
I am open for any comments or suggestions for the resolution of this issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
I had a similar issue last week, however, it was happening when the relay got synchronized via SNTP. please check that.
In this case the solution was the firmware upgrade, please check that and contact your local support.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Thanks for the answer. The Synchronization is OK via SNTP. We test without the GPS and the issue persist.¿Do you know the firmware version upgraded/downgraded?
Link copied. Please paste this link to share this article on your social media post.