Sepam GOOSE

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Sepam GOOSE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Ivan_Puškaš_EC
Lieutenant Ivan_Puškaš_EC
Lieutenant

Posted: ‎2020-10-29 05:52 AM . Last Modified: ‎2023-05-30 10:00 PM

0 Likes
7
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-29 05:52 AM

Sepam GOOSE

Hi,

 

We have a problem on Sepam relay with GOOSE mechanism. In last few months, time to time (every 20-30 days) Sepam receive signal about Breaker fail (50BF) over GOOSE. Problem is that none of the other feeder/motor relays sends this signal on the network.

GOOSE Logic was checked many times and no error was found. SCD is attached in case anyone is wondering about the GOOSE logic. And logic is simple:

All LD0.EQU_GGIO1.Ind1 are connected to G403 on the bay that needs to receive it, and G403 is in Sepam defined as "External trip"

EQU_GGIO1.Ind1 is V1 in equation and it is just the confirmation that CB is racked in (Input I111): V1  = P50BF_1_3  AND I111 . (if CB is racked in 50BF trip signal is send over V1 to the network if appears)

 

So recap: Incomer sees G403 signal as value 1 and it trips the CB, but none of the feeders that can send signal to Ethernet, sends it. Both signals on feeder are checked, 50BF signal and Equation V1 signal, none appears in the feeder log. This just looks like G403 signal has no correct value in one moment.

This appeared and two-three different incomers but never in the same time. Always only one incomer detects the signal. Other two are OK at that moment.

 

So,

 

First: Did, anyone had similar problem with, let's say "phantom" signal in GOOSE messaging? And did you realize what was the problem?

 

Second: Is there a solution to fix this problem or to implement something to secure right GOOSE communication?

 

Third: We are not sure about the meaning of the few signals and it would be appreciated if you can explain it. Maybe they can be used to secure correct GOOSE messaging.

- Quality status: QD Value of the "quality of data" flag for that message

- Quality status: QR Value of the "quality of reception" flag for that message

- GOOSE indication - as GOOSE input in Sepam

- GOOSE reception Fault - as GOOSE input in Sepam

- any other signal that we missed and that ca be maybe usefull

 

If more information is needed we can provide it.

 

Best regards,

Attachments
Goose Sepam.rar
Labels
  • Labels:
  • Application cases
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2021-05-21 01:43 AM . Last Modified: ‎2021-05-21 01:58 AM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-05-21 01:43 AM

@Ivan_Puškaš_EC 

 

I not sure if you got it done already but I just saw this post. For sepam you must assign the goose quality in a separate goose input to avoid this issue, when goose quality goes bad.

 

At the CET850 it will display to you the stVal and q separately, you should assign each one in a separately Gx0x input and do an AND with these two signals via Logic as following:

 

50BF SEPAM.pngLOGICA 5BBF GOOSE SEPAM.png

 

 

Best Regards

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
SergioFLORIDA
Lieutenant SergioFLORIDA Lieutenant
Lieutenant

Posted: ‎2020-10-30 03:50 AM

0 Likes
6
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-30 03:50 AM

Dear @Ivan_Puškaš_EC 

 

I am the Global Product Manager of Sepam ranges, thank for sharing the details information.

I got the message you have post and I am sharing with R&D team.

Let us analise it, in case we need aditional information, you will receive a contact from Schneider Electric.

 

Best Regards,

 

Florida

Tags (1)
  • Tags:
  • english
Reply
SergioFLORIDA
Lieutenant SergioFLORIDA Lieutenant
Lieutenant

Posted: ‎2020-10-30 05:34 AM

0 Likes
5
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-30 05:34 AM

Dear @Ivan_Puškaš_EC 

I have send you a private message to request aditional information about topic.

 

Could you check if you received the message into PRIVATE section?

 

Best Regards,

 

FLORIDA

Tags (1)
  • Tags:
  • english
Reply
Ivan_Puškaš_EC
Lieutenant Ivan_Puškaš_EC
Lieutenant

Posted: ‎2020-10-30 06:16 AM

0 Likes
0
1181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-30 06:16 AM

Dear @SergioFLORIDA 

 

Thank you for investigation.

 

I will send you all that you asked in PVT message.

 

BR

 

Tags (1)
  • Tags:
  • english
Reply
Ivan_Puškaš_EC
Lieutenant Ivan_Puškaš_EC
Lieutenant

Posted: ‎2020-11-03 04:29 AM

0 Likes
3
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-03 04:29 AM

@SergioFLORIDA 

Thanks for the help.

 

While we are waiting for the experts answer...

 

Can someone explain meaning of these signals in Sepam:

 

For GOOSE messaging (CET850)

- Quality status: QD Value of the "quality of data" flag for that message

- Quality status: QR Value of the "quality of reception" flag for that message

For those signals it is not clear for me what is the right meaning and use for them.

 

As "GOOSE input assignment" in drop down list in Sepam settings - GOOSE (SFT2841) 

- GOOSE indication - as GOOSE input in Sepam

- GOOSE reception Fault - as GOOSE input in Sepam

And for this signals I cant find any explanation in manuals that I have or that I found online.

 

Best regards

 

Tags (1)
  • Tags:
  • english
Reply
ChristopheCasa
Lt. Commander ChristopheCasa Lt. Commander
Lt. Commander

Posted: ‎2020-11-03 05:16 AM

2 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-03 05:16 AM

Hello,

I can not help too much but some information about the Quality status.

 

In normal operation, QR and QD should always equal to 0. Here below is an extract of the manual

  • QR: Quality Reception
    If at run time the QR attribute is set to1, this means that the GOOSE message was not received in the expected time.
  • QD: Dataset consistency
    If at run time the QD attribute is set to 1, this means that the structure of the GOOSE message is not as expected at subscription time.

 

So you can monitor QR and QD to detect a problem on a goose (not received or not well-formed)

 

Tags (1)
  • Tags:
  • english
Reply
Ivan_Puškaš_EC
Lieutenant Ivan_Puškaš_EC
Lieutenant

Posted: ‎2021-02-22 05:13 AM

0 Likes
1
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-22 05:13 AM

Just to complete the topic:


QR: Quality Reception, in SFT2841 setting this signal is named "GOOSE reception fault"


QD: Dataset consistency. in SFT2841 setting this signal is named "GOOSE reception indicator"

 

 

BR

Tags (1)
  • Tags:
  • english
Reply
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2021-05-21 01:43 AM . Last Modified: ‎2021-05-21 01:58 AM

0 Likes
0
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-05-21 01:43 AM

@Ivan_Puškaš_EC 

 

I not sure if you got it done already but I just saw this post. For sepam you must assign the goose quality in a separate goose input to avoid this issue, when goose quality goes bad.

 

At the CET850 it will display to you the stVal and q separately, you should assign each one in a separately Gx0x input and do an AND with these two signals via Logic as following:

 

50BF SEPAM.pngLOGICA 5BBF GOOSE SEPAM.png

 

 

Best Regards

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of