Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
Prerequisites
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
If your SmartConnect-compatible UPS is installed in an enterprise location, it may require additional network configuration to allow your UPS to connect to Schneider Electric cloud services.
IPv4 DHCP Server
An APC Smart-UPS device requires an IPv4 DHCP server on its network to assign an IPv4 address to the device so it can connect to the Internet.
Network MTU
The router and switch on the network of the APC Smart-UPS device must support a Maximum Transmission Unit (MTU) size of 336 bytes, at a minimum.
Network Firewall and Proxy Server
Schneider Electric strongly recommends that the device is not exposed to the public internet and is deployed behind an appropriate Stateful Packet Inspection (SPI) firewall.
To connect to Schneider Electric cloud services, the UPS needs to be able to connect directly to TCP port 443 on cece.prod.struxurewarecloud.com AND lwm2m.na.struxurewarecloud.com.
If the network of the UPS is behind a proxy server (e.g. ZScaler), you must add a firewall rule that permits this connection to TCP port 443, and bypasses any proxy service packet inspection. Consult with your Network Administrator to configure this firewall rule.
Network Switch Port Speed
SmartConnect-compatible UPS devices only support 10/100 Mbps port speed. If you are using a 1Gb network switch, and the port is not set to auto-configure its speed, this can prevent the device from connecting to Schneider Electric cloud services.
Network Devices Connected to the UPS
NOTE: If your UPS is providing power protection to network devices (e.g. network switch, router) connected to an outlet group:
Do not configure outlet group shutdown for that outlet group in response to UPS events, via PowerChute Network Shutdown, or PowerChute Serial Shutdown.
Do not configure Load Shedding for that outlet group.
If the network devices that provide internet connectivity to the UPS are turned off during a UPS event:
Schneider Electric cloud services are not informed of the event, due to the loss of internet connectivity.
UPS events, including those that trigger Load Shedding or shutdown as configured in PowerChute, are not displayed on the web portal status page, or in the event log, and no event email notifications are sent.
As a result, the web portal cannot inform you that UPS events are occurring, and if power is not restored to the network devices, a "Communication Lost" event occurs. See Critical UPS Events for more information.
Enabling cloud writes to your Smart-UPS
The SmartConnect feature for UPS reporting and remote monitoring is permitted on most Smart-UPS by default [SmartConnect: Enable-No Ctrl]. This allows you to view important data from your APC Smart-UPS and receive notifications.
Remote firmware installation commands, Advanced plan features, self test, and sensitivity adjustment all require SmartConnect to be permitted with Control [SmartConnect: Enable-With Ctrl].
To enable 'SmartConnect Control', also called 'SmartConnect access' on your UPS, consult your user manual. Use the LCD screen on the device or a lever at the rear of the device (e.g. SCL models).
UPS models with prefix SMT, SMC, SCL, SMX, SMTL, and SRTL, that have a SmartConnect Ethernet port.
These models have an APC SmartConnect Ethernet port that you can use to connect the UPS to Schneider Electric cloud services.
NOTE: Physical access to your Smart-UPS is required to scan the QR code label to register your device, and to adjust the ‘SmartConnect Control’ permission on the Smart-UPS which governs how your UPS interacts with the cloud system. Find out more about SmartConnect Control.