Total Rated-Current Distortion and ION 8650 Meters

Power Monitoring and Energy Automation NAM

This forum is created for the exchange of information and open dialogue regarding electrical power monitoring and energy automation products and services. Participants will have access to downloadable material as well as chat opportunities with subject matter experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution NEMA
  • Power Monitoring and Energy Automation NAM
  • Total Rated-Current Distortion and ION 8650 Meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
7
Michael_Neas
Ensign Michael_Neas Ensign
3
Robert_Lee
Admiral Robert_Lee Admiral
2
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Monitoring and Energy Automation NAM
Start a Topic
N4th4n13L
Lieutenant JG N4th4n13L Lieutenant JG
Lieutenant JG

Posted: ‎2021-03-05 09:17 AM

1 Like
0
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-05 09:17 AM

Total Rated-Current Distortion and ION 8650 Meters

TRD is Total Rated-Current Distortion and is the total root-sum-square of the current distortion components (including harmonics and inter-harmonics) created by the DER unit expressed as a percentage of the DER rated currenting capacity (Irated). As defined in IEEE 1547-2018. The term is also being adopted in IEEE 2800P with a slight difference. These standards are for monitoring Distributed Energy Resources and Inverter-Based Resources on the Transmission System. 

First, what are the differences in TRD between the 2 standards;

 

%TRD = √(Irms2 – I12) /Irated * 100%

 

In IEEE Std 1547 where;

I1             is the fundamental current as measured at the reference point of applicability (RPA).

Irated         is the distributed energy resource (DER) rated current capacity (transformed to the RPA when a transformer exists between the DER unit and the RPA)

Irms          is the root-mean-square of the DER current, inclusive of all frequency components, as measured at the RPA.

 

In IEEE Std P2800 where;

I1             is the fundamental current as measured at the reference point of applicability (RPA).

Irated         is the inverter-based resource (IBR) plant rated current capacity based on IBR plant MVA rating at the RPA (calculated based on the interconnection request) without any shunt devices installed as part of the installed project.

Irms          is the root-mean-square of the IBR plant current, inclusive of all frequency components up to the 50th order, as measured at the RPA.

 

The main difference between the two standards is how RMS is defined. Since, 1547 defines Irms as inclusive of all frequency components it is possible to calculate TRD in the 8650C, 8650B, and 8650A models. For, 2800P as defined above, will require an 8650A meter to perform the calculations.

What is needed to calculate TRD per 1547?

  • Irms can be obtained from the Power Meter module output registers. Values are in primary amps.
  • Irated can be entered using an External Number Register. Enter value in primary amps.
  • I1 is obtained from the Power Harmonics Module (8650A/B/C) or Harmonic Measurement Modules (8650A). Values are in primary amps.

How to execute?

Create an arithmetic module to be used for the calculations.

Input Registers

Setup Registers

Output Registers

Source 1: I arms

ART Formula 1: (sqrt(S1^2-S2^2)/S7 * 100

ART Result 1: I a %TRD

Source 2: I a1

ART Formula 2: (sqrt(S3^2-S4^2)/S7 * 100

ART Result 2: I b %TRD

Source 3: I brms

ART Formula 3: (sqrt(S5^2-S6^2)/S7 * 100

ART Result 3: I c %TRD

Source 4: I b1

 

 

Source 5: I crms

 

 

Source 6: I c1

 

 

Source 7: Irated

 

 

 

What is needed to calculate TRD per OP2800?

  • Irms can be obtained from the Power Quality Analyzer module output registers. Values are in primary amps, and you can select 150/180 cycle or 10m values.
  • Irated can be entered using an External Number Register. Enter value in primary amps.
  • I1 is obtained from the Harmonic Measurement Modules (8650A). Values are in primary amps and will be 150/180 cycle or 10m value depending on Aggregation method of the module.

How to execute?

Create an arithmetic module to be used for the calculations.

Input Registers

Setup Registers

Output Registers

Source 1: I arms

ART Formula 1: (sqrt(S1^2-S2^2)/S7 * 100

ART Result 1: I a %TRD (150/180 Cycle or 10m)

Source 2: I a1

ART Formula 2: (sqrt(S3^2-S4^2)/S7 * 100

ART Result 2: I b %TRD (150/180 Cycle or 10m)

Source 3: I brms

ART Formula 3: (sqrt(S5^2-S6^2)/S7 * 100

ART Result 3: I c %TRD (150/180 Cycle or 10m)

Source 4: I b1

 

 

Source 5: I crms

 

 

Source 6: I c1

 

 

Source 7: Irated

 

 

 

Once, you have the values calculated you can connect them the in a data recorder or incorporate in other frameworks.

For more information reach out to your Schneider Electric Utility Account Executive, Regional Manager or local Sales Representative.

Labels
  • Labels:
  • ION 8650
  • Power Quality
  • Utility Events
  • Utility Metering
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore