Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82169members
349759posts

Open Phase Feature Documentation for Form 9S 8650's

Power Monitoring and Energy Automation NAM

This forum is created for the exchange of information and open dialogue regarding electrical power monitoring and energy automation products and services. Participants will have access to downloadable material as well as chat opportunities with subject matter experts.

Solved
Bill_Mulkey
Crewman
Crewman
0 Likes
5
900

Open Phase Feature Documentation for Form 9S 8650's

Where can I find documentation on the Open Phase feature for the 9S Blade powered 8650 meters? 

Tags (1)

Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
4
891

Re: Open Phase Feature Documentation for Form 9S 8650's

Hello @Bill_Mulkey ,

 

I am not sure about any official documents but perhaps I can answer your question(s). To start this framelet was designed to account for a very specific use case, ION8650 meter with blade power Wye-connected 3-phase system.

 

The objective of the Open Phase Detection Framework is to identify an open phase condition. Additionally, if enabled, the framework will clamp the kW, kVAR, and kVA reading on the open phase(s) to zero and remove the open phase(s) from the energy accumulation calculation. 

 

Detection of an open phase is done using symmetrical components in conjunction with phase voltage compared to V nominal and V average. 

 

If you need more information please let me know.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
5 Replies 5
Charles_Murison
Picard Picard
Picard
0 Likes
4
892

Re: Open Phase Feature Documentation for Form 9S 8650's

Hello @Bill_Mulkey ,

 

I am not sure about any official documents but perhaps I can answer your question(s). To start this framelet was designed to account for a very specific use case, ION8650 meter with blade power Wye-connected 3-phase system.

 

The objective of the Open Phase Detection Framework is to identify an open phase condition. Additionally, if enabled, the framework will clamp the kW, kVAR, and kVA reading on the open phase(s) to zero and remove the open phase(s) from the energy accumulation calculation. 

 

Detection of an open phase is done using symmetrical components in conjunction with phase voltage compared to V nominal and V average. 

 

If you need more information please let me know.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Bill_Mulkey
Crewman
Crewman
0 Likes
3
882

Re: Open Phase Feature Documentation for Form 9S 8650's

@Charles_Murison,

 

Thank you for the response and clarification. Good information. ION Setup only has a small description of the feature under Open Phase and it doesn't specify Wye or Delta service types, only "9S blade powered devices". 

Tags (1)
Charles_Murison
Picard Picard
Picard

Re: Open Phase Feature Documentation for Form 9S 8650's

Hello Bill,

 

Thank you for the feedback, I will forward this on to the ION Setup developer.

 

Regards,
Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
sesa29811
Crewman Crewman
Crewman
0 Likes
1
867

Re: Open Phase Feature Documentation for Form 9S 8650's

@Charles_Murison  @Bill_Mulkey 

Yes I have ran across this issue on a Navy site with 8650C model . I had no voltage on A phase but the meter still calculated the phase as if its still there. The only way I noticed that was that the phasor was really funky. I then tested with my fluke meter and found it was dead at the A phase but voltage lead pickup was inside the transformer itself. The meter was still calculating Kw and Kwh normally since it saw the amps on that phase. Not sure that's a good thing other than for billing?

Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
0
857

Re: Open Phase Feature Documentation for Form 9S 8650's

Hello David,

 

This is the exact reason why the open phase feature was developed for blade powered meters.

 

Regards,

Charles