Posted: 2023-05-30 09:09 PM
A PME 2022 server was installed on a network with approx. 50 existing ION meters (7350, 7400, 8000). These meters backfilled historical data and the database was trimmed. However, Events and Alarms were not removed from the database as the PME2022 TrimRecords stored procedure has a check for AcknowledgementID. Has anyone tested using the PME2021 TrimRecords SP on the new software version?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-02 10:38 AM . Last Modified: 2023-06-02 10:55 AM
Hello @RdM ,
I have never tried using PMe2021 TrimRecords store procedure on PME 2022 system. Possible the Store procedure does not have instructions to remove tables that may have been created in PME 2022 or changed to include a link to new or different tables.
One option would be to remove the "and a.AcknowledgementID IS NULL" from the TrimRecords
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-02 10:38 AM . Last Modified: 2023-06-02 10:55 AM
Hello @RdM ,
I have never tried using PMe2021 TrimRecords store procedure on PME 2022 system. Possible the Store procedure does not have instructions to remove tables that may have been created in PME 2022 or changed to include a link to new or different tables.
One option would be to remove the "and a.AcknowledgementID IS NULL" from the TrimRecords
Regards,
Charles