What is the maximum allowable temperature on the terminals of a MTZ ACB?
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-06 11:53 PM
hello @cdurand
this point is define on the IEC 60-947-1
On a Brand new product, for silver contact (case of MTZ) maximum temperature on terminals is 110°C maximum.