ATS contactors sizing

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • ATS contactors sizing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
66
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
h171
h171
Cadet

Posted: ‎2023-03-22 01:05 PM

0 Likes
2
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 01:05 PM

ATS contactors sizing

Hello

I want to use two contactors to design an automatic transfer switch (ATS) between utility and generator sources with 3X32 Amps capacity.

the load type that I will connect to the output of the ATS is lighting, heaters, Air conditioning, 1 kW water pump, and power sockets for the kitchen, laptop and etc...

for sizing the two contactors shall I do the following:

- The contactor size should be equal to or more than the 32 Amp source rating.

- shall I use a 3 or 4-pole contactor and why?

- shall I size the contactor based on the AC-1 or AC-3 rating?

could you please provide me an answer with a reference?

 

I really appreciate any help you can provide.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2023-03-31 02:27 AM . Last Modified: ‎2023-03-31 02:32 AM

1 Like
0
1092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-31 02:27 AM . Last Modified: ‎2023-03-31 02:32 AM

Hello @h171 ,

 

Have you looked at: Discover-TransferPacT-Automatic-The-new-Generation-of-All-in-one/ Post from Schneider Electric? Some good and nice information about the automatic transfer pacts from Schneider Electric.

The questions you are asking about the poles are not really for us to answer, but for your net supplier and regulations etc.
It depends on what type of distribution system you get inside your building and what type of system you want to keep going into the building; TN-C, TN-S or TT.

If you are only talking about the contactor being 3 or 4 pole. In our country we have certain regulations regarding using contactors for by instance an emergency stop.
In this case (emergency stop) you always have to fully switch the installation off, that is including the N (Null-zero) so in that case you always need a 4 pole contactor.

Also your question related to the AC-1 or AC-3 contator and usage, I think this page might help you out with that; AC1 vs AC3 (For short reference it has to do with what kinda load you are using the contactor for, light loads or industrial loads).

Hope this has given you some valuable insight and info!


Kind regards,

Rick

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2023-04-06 11:48 PM

0 Likes
0
1058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-06 11:48 PM

Hello @h171 

completly aligned with @RHH.

Don't try to design yourself an ATS, you will take to big risk about the safety aspect. 

Our ATS garanty on eatch case of application to be safe.

Gregoire Brun
Breaker Product Expert

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2023-03-31 02:27 AM . Last Modified: ‎2023-03-31 02:32 AM

1 Like
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-31 02:27 AM . Last Modified: ‎2023-03-31 02:32 AM

Hello @h171 ,

 

Have you looked at: Discover-TransferPacT-Automatic-The-new-Generation-of-All-in-one/ Post from Schneider Electric? Some good and nice information about the automatic transfer pacts from Schneider Electric.

The questions you are asking about the poles are not really for us to answer, but for your net supplier and regulations etc.
It depends on what type of distribution system you get inside your building and what type of system you want to keep going into the building; TN-C, TN-S or TT.

If you are only talking about the contactor being 3 or 4 pole. In our country we have certain regulations regarding using contactors for by instance an emergency stop.
In this case (emergency stop) you always have to fully switch the installation off, that is including the N (Null-zero) so in that case you always need a 4 pole contactor.

Also your question related to the AC-1 or AC-3 contator and usage, I think this page might help you out with that; AC1 vs AC3 (For short reference it has to do with what kinda load you are using the contactor for, light loads or industrial loads).

Hope this has given you some valuable insight and info!


Kind regards,

Rick
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2023-04-06 11:48 PM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-06 11:48 PM

Hello @h171 

completly aligned with @RHH.

Don't try to design yourself an ATS, you will take to big risk about the safety aspect. 

Our ATS garanty on eatch case of application to be safe.

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now